For what its worth, in the 2013 code cycle of NFPA 13, I submitted two
proposed changes related to this topic.  The first was to eliminate
sprinklers directly above the water where indoor swimming pools were
present.  This was rejected by the committee with the statement that indoor
pools are not always in service and when drained, could be used for
storage - so sprinklers are required above the pool.

The second proposal was to eliminate sprinklers in gymnasium locker room
shower areas where non-combustible tiles covered the entire floor, walls and
ceilings. This was also rejected by the committee with the statement that
gym mats and similar combustibles could be stored in these areas.

Additional discussion related to swimming pools expressed concerns for
combustible play toys and equipment often found in swimming pools.  Yes, I
did argue that changes of occupancy or use are addressed by NFPA 25 and
addressed the corrosive nature of the environment on the sprinklers, but the
committee rejected the proposal to omit sprinklers above the indoor pool.


Bob Caputo, CFPS
President
American Fire Sprinkler Association

Expand your business with ITM.
Professionalize the role of your inspection team with AFSA’s comprehensive
20-month ITM Inspector Development program that provides a blended learning
environment teamed with robust curriculum created by top industry leaders.
Now enrolling for Spring 2022!


-----Original Message-----
From: Sprinklerforum <[email protected]> On
Behalf Of Tony Silva via Sprinklerforum
Sent: Sunday, February 6, 2022 10:06 PM
To: [email protected]
Cc: Tony Silva <[email protected]>
Subject: Re: swimming pool

Thanks for the responses. I'm trying to find out the industry practice.
Which do you see more? Sprinklers below the water slides or none taking into
account the fire load and possible vandalism?
Tony

On Fri, Feb 4, 2022 at 5:31 PM AKS-Gmail-IMAP via Sprinklerforum <
[email protected]> wrote:

> That is the preferred way to set the AHJ agreement, in distributed
> meeting minutes of course, because the other way it may be set,
> “provide NFPA 13 coverage for the deck area only”, means some
> sprinklers have to be installed beyond the pool edge to satisfy the
> application density transition boundary rules. That’s why it is best
> to be present at that first AHJ meeting, not just the Architect like some
> Architects like to do.
> The AHJs appreciate being in on the design from inception when dealing
> with odd situations.
>
> >
> > I have seen a pool where it was the AHJ that specifically required
> > NO
> heads anywhere over a pool because they are impossible to maintain.
> (municipal facility)
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to