Was on vacation for a couple days so still catching up on the emails.

What Rick said.   FFs won’t use the hose on a small hose connection or Class 2 
(like, EVER) but they might use the valve, particularly if it’s downstream of 
the FDC so they can control the water supply.   A last resort for attack line 
water supply, mostly perceived as a mop-up stream.


The foregoing is my opinion only and does not represent NFPA or the NFPA 14 
Technical Committee, nor intended to serve as an interpretation of the standard.

Protection Design and Consulting
Steve Leyton, President
T  |  619.255.8964 x 102  |  
www.protectiondesign.com<http://www.protectiondesign.com/>
2851 Camino Del Rio South  |  Suite 210  |  San Diego, CA  92108
Fire Protection System Design | Consulting | Planning | Training








From: Rick Matsuda <[email protected]>
Sent: Monday, August 08, 2022 2:34 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Hose Valves

Ben,
Since nobody is responding to you question, I’ll give you my best opinion which 
has nothing to do with what the code may state.

If there is hose and nozzle attached to the 1 1/2-inch hose valves, then I 
would think they’re provided for tenant use in addition to a fire extinguisher. 
However, unless the employees are trained to use the hose, the company would 
probably not ask them to attempt to fight a large fire due to liability issues. 
Get out and call the fire department.
Also, if there is hose attached, I don’t think a fire department would use the 
hose for fire fighting operations because they don’t know the condition of the 
hose.

If there is no hose provided, then I think the hose valves are there for the 
fire department cleanup/mop up operations. I don’t think that they would enter 
a fire fighting area dragging their own hose and looking for a valve to hook up 
to.

As stated above, these are just my opinions so I hope I don’t upset anyone.
Rick Matsuda


On Aug 8, 2022, at 1:40 PM, Ben Hill <[email protected]<mailto:[email protected]>> 
wrote:

What is the purpose of 1 ½” Hose Valves in a warehouse?  Is it to actually 
fight fire, of for cleanup?


Ben Hill

Yadkin Valley Fire Protection, Inc.
142 Commercial Park Dr.
Thomasville, NC 27360

Cell 336-580-5064
[email protected]<mailto:[email protected]>



_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to