Hi,
Great forum. My question is I have a business warehouse S-1. That is fully 
sprinklered. The owner put in walk in coolers and freezers years ago. I related 
that due to the fact he is fully sprinklered he would need to put in protection 
for all the walk in coolers and freezers.We use IFC 2015. What code can I 
reference? Thanks

From: Fpdcdesign [mailto:[email protected]]
Sent: Tuesday, August 30, 2022 7:07 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: NFPA 291 25% Drop

Chris,

I think part of it is practicality. There are some situations where to get a 
25% drop, you are going to have to drain the water tower. Also, with water 
companies that are doing their own tests with a couple of field guys, they are 
not going to open a bunch of hydrants; one and done.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-554-7054<tel:860-554-7054>  (fax)
860-608-4559<tel:860-608-4559> (cell)



On Aug 30, 2022 at 5:21 PM, <Christopher Cahill<mailto:[email protected]>> 
wrote:
Good day all, it’s been a while.  I’m still here for you old timers.

It appears the traditional 25% drop in residual pressure for satisfactory 
results has been modified to 10%, ’22 edition 4.4.6.  I’ve looked in the 
committee reports and can’t find why.  When I look in the enhanced content on 
Link it talks about 25% still.  So now I’m wondering if it’s a typo. Anyone 
have an idea why this changed?

The option to flow system demand appears modified as well in 4.4.7 When 
conducting a flow test for the purpose of fire protection system design, the 
flow and pressure results should be adequate for the total demand of the 
system.  Like that’s practical for high demand systems, lol.

Putting it together does it all mean for fire flow drop 10% and for system 
design we now HAVE to go to system demand?

Chris Cahill, PE* \ Burns & McDonnell
Sr. Associate Fire Protection Engineer
Phone: 952.656.3652
[email protected]<mailto:[email protected]>

*Registered in: MN

[A close up of a sign    Description automatically 
generated]<https://www.burnsmcd.com/insightsnews/industries/construction?utm_campaign=CORP_NationalConstruction&utm_source=OutlookSignatures_Web-InsightsNews-Industry-Construction>

_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To 
unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to