NFPA 13, 2013 Chapter 8
in a nut shell, ALL areas of a building shall be protected unless
specifically omitted by NFPA 13
Coolers and Freezers do not have an exception or exclusion anywhere in the
code to allow sprinklers to be omitted in them
If you have the handbook there is more discussion in detail about this that
specifically talks about coolers and freezers having no exclusions from
protection, or the annex - A8.1.1
I believe the fire code refers to NFPA 13 for all sprinkler related codes.

Thanks

Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
[email protected]
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718 2676 24h
Visit us at www.proudline.ca

Proudline now offers ULc listed monitoring services, please contact
[email protected] for more information






On Wed, Aug 31, 2022 at 6:20 AM Thomas Reinhardt <[email protected]>
wrote:

> Hi,
>
> Great forum. My question is I have a business warehouse S-1. That is fully
> sprinklered. The owner put in walk in coolers and freezers years ago. I
> related that due to the fact he is fully sprinklered he would need to put
> in protection for all the walk in coolers and freezers.We use IFC 2015.
> What code can I reference? Thanks
>
>
>
> *From:* Fpdcdesign [mailto:[email protected]]
> *Sent:* Tuesday, August 30, 2022 7:07 PM
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> [email protected]>
> *Subject:* [Sprinklerforum] Re: NFPA 291 25% Drop
>
>
>
> Chris,
>
>
>
> I think part of it is practicality. There are some situations where to get
> a 25% drop, you are going to have to drain the water tower. Also, with
> water companies that are doing their own tests with a couple of field guys,
> they are not going to open a bunch of hydrants; one and done.
>
>
>
> Todd G Williams, PE
>
> Fire Protection Design/Consulting
>
> Stonington, CT
>
> 860-535-2080 (ofc)
>
> 860-554-7054  (fax)
>
> 860-608-4559 (cell)
>
>
>
>
> On Aug 30, 2022 at 5:21 PM, <Christopher Cahill <[email protected]>>
> wrote:
>
> Good day all, it’s been a while.  I’m still here for you old timers.
>
>
>
> It appears the traditional 25% drop in residual pressure for satisfactory
> results has been modified to 10%, ’22 edition 4.4.6.  I’ve looked in the
> committee reports and can’t find why.  When I look in the enhanced content
> on Link it talks about 25% still.  So now I’m wondering if it’s a typo.
> Anyone have an idea why this changed?
>
>
>
> The option to flow system demand appears modified as well in 4.4.7 When
> conducting a flow test for the purpose of fire protection system design,
> the flow and pressure results should be adequate for the total demand of
> the system.  Like that’s practical for high demand systems, lol.
>
>
>
> Putting it together does it all mean for fire flow drop 10% and for system
> design we now HAVE to go to system demand?
>
>
>
> *Chris Cahill, PE** \ Burns & McDonnell
>
> Sr. Associate Fire Protection Engineer
>
> Phone: 952.656.3652
>
> [email protected]
>
>
>
> *Registered in: MN
>
>
>
> [image: A close up of a sign Description automatically generated]
> <https://www.burnsmcd.com/insightsnews/industries/construction?utm_campaign=CORP_NationalConstruction&utm_source=OutlookSignatures_Web-InsightsNews-Industry-Construction>
>
>
>
> _________________________________________________________ SprinklerForum
> mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to