How much higher is the pressure and where is the base of the riser compared to 
the location of the gauge?

Pete

From: Brad Casterline <[email protected]>
Sent: Monday, September 26, 2022 9:48 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: [EXTERNAL] Re: Pressure on placard greater that 
static.

A Main Drain Test would be interesting if this was the case!
The pressure would drop as the valve is being opened, then at some point start 
climbing.
Most ‘everyday’ system demands can be flowed out the Main Drain, especially if 
it is 2”.
I’ve never seen or heard of a Main Drain Test where the residual is higher than 
the static, but then, I don’t get out much.
I think step 1 in trouble shooting this water supply quandary is to verify the 
gauge is working right.
I know we record Main Drain Tests to keep our eye on the water supply over 
time, and nowadays we can use them to estimate the flow when exercising a BFP.

Brad

From: Matthew J Willis <[email protected]<mailto:[email protected]>>
Sent: Thursday, September 22, 2022 4:37 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [EXTERNAL] [Sprinklerforum] Re: Pressure on placard greater that 
static.

Might be some city pumps kicking in you do not know about.

R/
Matt


Matthew J. Willis, CWBSP
Design Manager

Rapid Fire Protection, Inc.
600 E. Carlson St. Suite AB | Cheyenne, WY. 82009
Office (307) 426-4077 ext. 404
Direct (307) 316-6630
Cell (605) 391-2733
[cid:[email protected]]


From: Fpdcdesign <[email protected]<mailto:[email protected]>>
Sent: Thursday, September 22, 2022 2:23 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Pressure on placard greater that static.

I have run into a couple of situations where the required pressure as shown on 
the system placard is less than the static pressure on the riser. I found 
another one today during a survey. If others are finding this, how do they 
handle it?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-554-7054<tel:860-554-7054>  (fax)
860-608-4559<tel:860-608-4559> (cell)
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to