Matt- Sweeeeet. Thank you! I've never ran into this before but your solution is way cheaper.
Brian Harris, CET BVS Systems Inc. bvssytemsinc.com<http://bvssystemsinc.com/> From: Matt Grise <[email protected]> Sent: Thursday, November 10, 2022 9:23 AM To: Discussion list on issues relating to automatic fire sprinklers <[email protected]> Subject: [Sprinklerforum] Re: Vertical Inline Pump Suction No need for that. Just give it the old "up over and down". We run into that frequently with 2000 gpm pumps on 8" underground lines also. Matt From: Brian Harris <[email protected]<mailto:[email protected]>> Sent: Thursday, November 10, 2022 8:06 AM To: [email protected]<mailto:[email protected]> Subject: [Sprinklerforum] Vertical Inline Pump Suction Sizing a pump for an existing warehouse, 85psi @ 1500gpm, calls for 8" flanges. NFPA-20 (2013), 4.14.3.3 states 10 pipe diameters upstream of suction flange. Existing stub-up is 6", safe to assume some underground work is in order? Brian Harris, CET BVS Systems Inc. Design Manager bvssystemsinc.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fbvssystemsinc.com%2f&c=E,1,DeWZumQxrku2OLg2gaqnn8k2Q7MkTzk5aEQYjCQOW5TWlrY7F8eFi7lYBXnDZlfy5f2iFgzPCfyR2a0e6GoKPUjO3qX3cEI5AVrVDTpmzRVjaO-xmJggSmk,&typo=1> Phone: 704.896.9989 Fax: 704.896.1935