As much as I dislike taking a different position from you on any issue Ryan, I see the provisions of §17.4.5.5 quite differently than the one you've taken.

I believe that what  Dennis has told us is that clamps are in place to support the drops "to the walls".  Speculating that those clamps are roughly halfway down or up each side that would make the distance between supports less than 25', as it would include the pipe stand.

And now that I review your thoughts carefully, Ryan I do note that if those clamps are _*not*_ in place then the risers are not supported properly per §17.4.5.5 as you noted.

How about some further clarification Dennis?
*Ken Wagoner, SET*
*Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235*
*Phone: (760) 745-6181 *
*Visit the website <https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>*
On 12/29/2022 3:20 PM, Hinson, Ryan wrote:

Dennis,

It appears that you have a 25-ft auxiliary system loop of 4” pipe from deck to grade and back which must be properly supported.  I think your reviewing engineer’s concern may justified with how this pipe is supported as you are at the maximum 25-ft vertical distance between hangers on vertical piping per NFPA 13 (2022) Section 17.4.5.5 and you actually have one 25-ft- and one 23-ft long vertical pipe stack.  Do you have hangers within 2 ft of the top of each of the drops per Section 17.4.5.1? Even so, this single pipe stand at the base appears to be supporting twice the normally anticipated pipe stand load due to loading distribution where the bottom support must be sufficient for the bottom half of two vertical pipes – totaling approximately 25 ft of 4” water-filled pipe…which is nearly twice the typical loading of a single support due to spacing limitations of the same. Assuming Sch 40 pipe, I get the following load this pipe stand must support:

                              (10.78 lbs/ft) * 25 ft * 5 + 250 lbs = 1597.5 lbs

It is my opinion that per Section 17.5.1, you must EITHER:

  * Use off-the-shelf components in accordance with their
    listings/listed loadings per Sections 17.5.2 through 17.5.7 whose
    listings are further explained in Section A.17.1.6.1 for the load
    indicated above.

OR

  * Obtain hanger configuration certification from a licensed PE which
    includes all the mandates in Section 17.5.1.2.

Hope this helps,

*Ryan L. Hinson**, PE*, SET***\  Burns & McDonnell

Associate Fire Protection Engineer

*O*612-900-3755\ *M*763-688-4045 \ *F*952-229-2923

[email protected] <mailto:[email protected]>\ burnsmcd.com <http://www.burnsmcd.com/>

8201 Norman Center Drive, Suite 500  \  Minneapolis-St. Paul, MN 55437

*Registered in: AK, LA, MD, MN, PA, TX, & UT

**NICET IV - Water-Based Systems Layout

*From:* Dennis Wilson <[email protected]>
*Sent:* Thursday, December 29, 2022 1:53 PM
*To:* Discussion list on issues relating to automatic fire sprinklers <[email protected]>
*Subject:* [Sprinklerforum] Re: Pipe Stands

Thanks ken, I’ve read the chapter. But this is the architect/engineer from hell.

He has disapproved every submittal from every trade several times over, causing extreme delays, and everyone is banging their head against the wall.

He wants proof, and I’m not sure how to go about figuring out an equation.

Dennis Wilson

Blackhawk Auto. Sprinklers

Cedar Falls, Iowa

1-319-266-7721

*From:* Ken Wagoner <[email protected]>
*Sent:* Thursday, December 29, 2022 12:51 PM
*To:* [email protected]
*Subject:* [Sprinklerforum] Re: Pipe Stands

Dennis,

You did not indicate which edition of -13 is applicable, however some good supporting information can be found in the 2019 edition in §17.5 regarding pipe stands.  Make sure to read all of it, as it allows but does not require certification by a registered PE.

As I am a principal member of the committee on hanging and bracing, please see the disclaimer below.

have a safe and Happy New Year to everyone,

*Ken Wagoner, SET*
*Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235*
*Phone: (760) 745-6181 *
*Visit the website

* <https://nam12.safelinks.protection.outlook.com/?url=https%3A%2F%2Flinkprotect.cudasvc.com%2Furl%3Fa%3Dhttp%253a%252f%252fwww.parsleyconsulting.com%252f%26c%3DE%2C1%2CY5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK%26typo%3D1&data=05%7C01%7Crhinson%40burnsmcd.com%7C51b9610456774ef27aeb08dae9d66336%7Cbfbb9a2b6d994e78b3c795005d555c8b%7C0%7C0%7C638079404371146512%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C2000%7C%7C%7C&sdata=PaOTnaQgQl8pM%2BtlKA4GfJNQs%2F1SPTBpBLLgrYaLFjQ%3D&reserved=0>

*IMPORTANT NOTICE: This correspondence is not a Formal Interpretation issued pursuant to NFPA Regulations. Any opinion expressed is the personal opinion of the author and does not necessarily represent the official position of the NFPA or its Technical Committees. In addition, this correspondence is neither intended, nor should it be relied upon, to provide professional consultation or services

It should be noted that the above is my opinion as a member of the NFPA Automatic Sprinkler System Hanging and Bracing Committee and the Hanging and Bracing for Fire Suppression Systems Committee in accordance with the NFPA Regulations Governing Committee Projects and should therefore not be considered, nor relied upon, as the official position of the NFPA or its Committees
*
On 12/29/2022 11:47 AM, Dennis Wilson wrote:

    I have a 4” main @ 30’ AFF, I drop down w/ 4” to a 12” arm-over
    then up to a b’fly va. & Aux. Dry Va., then proceed back up to 28’
    AFF to feed a dry system.

    On the 4x 1’-0” arm-over we installed a pipe stand. (the arm-over
    is 5-0 above the floor) We also use clamps to support the drops to
    the walls.

    The engineer is asking for proof that the pipe stand can support
    the load. This is install and hasn’t fallen is not enough proof.

    Anyone have a way this can be done?

    Dennis Wilson

    Blackhawk Auto. Sprinklers

    Cedar Falls, Iowa

    1-319-266-7721

    _________________________________________________________

    SprinklerForum mailing list:

    https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org  
<https://nam12.safelinks.protection.outlook.com/?url=https%3A%2F%2Flists.firesprinkler.org%2Flist%2Fsprinklerforum.lists.firesprinkler.org&data=05%7C01%7Crhinson%40burnsmcd.com%7C51b9610456774ef27aeb08dae9d66336%7Cbfbb9a2b6d994e78b3c795005d555c8b%7C0%7C0%7C638079404371302723%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C2000%7C%7C%7C&sdata=WiPrrfVsMVSKd8xZufmyENyyzCXuZ%2FLiLDKw1icFg4M%3D&reserved=0>

    To unsubscribe send an email [email protected]


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to