This seems like one of those great communication with AHJ/Owner opportunities.

A deck is an exterior projection. I am assuming the deck is wood, and no 
fire-resistant stuff.

The only thing height wise is the 24" for obstructions over 4 feet, and the 48" 
for stages, with stipulations.

IMHO, the spray pattern development is not as big a concern with properly 
spaced and the lower heights as suppression will most likely occur.

At 8 feet, there will Def be storage under them if this is a residential 
environment.

The sprinklers will more than likely serve as impingement type, as the channels 
formed by the studs, and the open nature negates proper ceiling jet.

R/
Matt


Please rate our customer 
service<https://survey.medallia.com/?emailsignature&fc=3539&bg=Fire%20and%20Fabrication>

Matthew J. Willis, CWBSP, CET
Engineering Designer IV
FERGUSON FIRE DESIGN, LLC
A Wholly Owned Subsidiary of Ferguson Fire & Fabrication, LLC
401 N 5th Street
Suite 448
Wausau, WI 54403
C: 307-236-8249
[email protected]<mailto:[email protected]>
www.FergusonFire.com<http://www.fergusonfire.com/>

From: Taylor Schumacher <[email protected]>
Sent: Wednesday, March 8, 2023 6:15 AM
To: '[email protected]' 
<[email protected]>
Subject: [Sprinklerforum] Low Decks

Is there any guidance on sprinkler protection under decks that are really close 
to finished grade? I have a 13 project with combustible decks that range from 1 
foot to 8 foot above finished grade. Common sense tells me these short ones 
won't allow spray pattern development and replacing/testing will be a nightmare 
but I have nothing to fall back on.

Thanks,


Taylor Schumacher
Security Fire Sprinkler<http://www.j-berd.com/>
1 Industrial Blvd | Sauk Rapids, MN 56379
Office: 320.656.0847 | Direct: 320.640.7050

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to