Taylor,

Rick is on the right track on this. Check out 9.2.2 in NFPA 13-2019. This 
section allows sprinkler omissions from underneath ground floors, exterior 
docks, and platforms, with your decks likely falling into the platform 
category. There are a few requirements, one being that the area is protected 
against debris accumulation like Rick mentioned. The other big one for you will 
be that the flooring over the space needs to be “of tight construction” which 
is nicely vague. If your decks are trex style, you will probably want to make 
sure that the board spacing is pretty close.

There isn’t a height stipulation in 9.2.2, so you are going to have to make a 
judgment call as to when this rule stops applying and 9.2.3 for exterior 
projections starts applying.

Personally, I would start to feel uncomfortable using this omission if the 
height below the deck gets to a point where someone could walk below them 
without needing to crawl.

Hope this helps!

Eric Rieve
Rieve Fire Protection

From: Rick Matsuda <[email protected]>
Sent: Wednesday, March 8, 2023 10:21 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Low Decks

As an old AHJ, I would require you to screen in any unsprinklered decks that 
are permitted to prevent accumulation of debris beneath them.
Rick Matsuda


On Mar 8, 2023, at 9:04 AM, 
[email protected]<mailto:[email protected]> wrote:

This seems like one of those great communication with AHJ/Owner opportunities.

A deck is an exterior projection. I am assuming the deck is wood, and no 
fire-resistant stuff.

The only thing height wise is the 24” for obstructions over 4 feet, and the 48” 
for stages, with stipulations.

IMHO, the spray pattern development is not as big a concern with properly 
spaced and the lower heights as suppression will most likely occur.

At 8 feet, there will Def be storage under them if this is a residential 
environment.

The sprinklers will more than likely serve as impingement type, as the channels 
formed by the studs, and the open nature negates proper ceiling jet.

R/
Matt


Please rate our customer 
service<https://survey.medallia.com/?emailsignature&fc=3539&bg=Fire%20and%20Fabrication>

Matthew J. Willis, CWBSP, CET
Engineering Designer IV
FERGUSON FIRE DESIGN, LLC
A Wholly Owned Subsidiary of Ferguson Fire & Fabrication, LLC
401 N 5th Street
Suite 448
Wausau, WI 54403
C: 307-236-8249
[email protected]<mailto:[email protected]>
www.FergusonFire.com<http://www.fergusonfire.com/>

From: Taylor Schumacher <[email protected]<mailto:[email protected]>>
Sent: Wednesday, March 8, 2023 6:15 AM
To: '[email protected]' 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Low Decks

Is there any guidance on sprinkler protection under decks that are really close 
to finished grade? I have a 13 project with combustible decks that range from 1 
foot to 8 foot above finished grade. Common sense tells me these short ones 
won’t allow spray pattern development and replacing/testing will be a nightmare 
but I have nothing to fall back on.

Thanks,


Taylor Schumacher
Security Fire Sprinkler<http://www.j-berd.com/>
1 Industrial Blvd | Sauk Rapids, MN 56379
Office: 320.656.0847 | Direct: 320.640.7050


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to