Todd,


Have you tried using a 4.2k sprinkler?  You aren’t using it to ‘balance the 
calcs’ but to control the over-discharge due to the small amount of area the 
sprinklers are covering.



Cliff Whitfield, SET

President



Fire Design, Inc.

940 Summerbrooke Dr

Tallahassee, FL 32312

Ph: 828-284-4772





From: Fpdcdesign <[email protected]>
Sent: Monday, March 27, 2023 3:08 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Too many sprinklers in the bathroom



I am working on a renovation to a college dormitory bathroom. The dorm rooms 
are around the perimeter and the common bathroom is in the central core. The 
college is replacing the existing partial height toilet and shower partitions 
with full height partitions with full height doors. This is in effect creating 
several small room, each requiring a sprinkler. The number of sprinklers in 
this 410 sqft space is increasing from 4 to 15. This will be a hydraulic 
nightmare. The rooms were designed to NFPA 13 Residential and I have not yet 
found a calc sign that included the bathroom. My guess is that the whole system 
would be undersized.



Since this is not in a dwelling unit and is on a common corridor, 9.2.4.1 does 
not apply.



Room design does not work because all of the sprinklers are either in the space 
or the communicating space.



I have to calculate a 1500 sqft area in order to eliminate the sprinklers in 
the stalls and showers.



Per Chapter 12, residential sprinklers can only be used in dwelling units and 
adjacent corridors, so that design is out.



Any thoughts?



Todd G Williams, PE

Fire Protection Design/Consulting

Stonington, CT

860-535-2080 <tel:860-535-2080>  (ofc)

860-554-7054 <tel:860-554-7054>   (fax)

860-608-4559 <tel:860-608-4559>  (cell)



--
This email has been checked for viruses by Avast antivirus software.
www.avast.com
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to