Craig, the language covers that.

R/
Matt

Please rate our customer 
service<https://survey.medallia.com/?emailsignature&fc=3539&bg=Fire%20and%20Fabrication>

Matthew J. Willis, CWBSP, CET
Engineering Designer IV
FERGUSON FIRE DESIGN, LLC
A Wholly Owned Subsidiary of Ferguson Fire & Fabrication, LLC
401 N 5th Street
Suite 448
Wausau, WI 54403
C: 307-236-8249
[email protected]<mailto:[email protected]>
www.FergusonFire.com<http://www.fergusonfire.com/>

From: Travis Mack <[email protected]>
Sent: Wednesday, April 5, 2023 10:01 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: [EXTERNAL] Re: Standpipes & FDC

That is from NFPA 14, 2019 edition.  Check the 2016 edition.  It’s there as 
well.


Travis Mack, SET
M.E.P.CAD |
181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074
www.mepcad.com<http://www.mepcad.com/> | m: 480.547.9348

AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD

Book appointment time in my calendar
https://calendly.com/t_mack_mepcad<https://calendly.com/t_mack_mepcad>

From: Prahl, Craig <[email protected]<mailto:[email protected]>>
Sent: Wednesday, April 5, 2023 8:59 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: [EXTERNAL] Re: Standpipes & FDC

Travis, what standard or code are you referencing?

I would question the requirement of providing supervisory air in a manual 
standpipe based on the language of 6.1.1 specifically addressing Dry 
standpipes.  A dry standpipe and a Manual standpipe are distinctly different.

Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$>
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS


From: Travis Mack <[email protected]<mailto:[email protected]>>
Sent: Wednesday, April 5, 2023 11:49 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: [EXTERNAL] Re: Standpipes & FDC

All dry standpipes,  including manual standpipes, are required to have 
supervisory air to help protect against that situation described.  This was 
added, I believe, in the 2016 edition.  This is a snip from the 2019 edition.

6.1.1 Location of Dry Standpipes.
Dry standpipes shall be monitored in accordance with NFPA 72 with supervisory 
air pressure.
ENHANCED CONTENT
Collapse
Standpipe systems, including standalone manual standpipes, need to be 
supervised to ensure proper operation and integrity of the system. Supervision 
can be achieved through central station, a constantly attended local station, 
or by a signal or local alarm at the initiating device attached to the 
standpipe system.




Travis Mack, SET
M.E.P.CAD |
181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074
www.mepcad.com<https://urldefense.com/v3/__http:/www.mepcad.com/__;!!B5cixuoO7ltTeg!FsG36-XDvOQrgI_DHQGIVDG6qG0wUDytk9o-fCPhFdG51_cdUp7u8R9b_hwGMfSVSUMQZ1YdU_uNHp9p$>
 | m: 480.547.9348

AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD

Book appointment time in my calendar
https://calendly.com/t_mack_mepcad<https://urldefense.com/v3/__https:/calendly.com/t_mack_mepcad__;!!B5cixuoO7ltTeg!FsG36-XDvOQrgI_DHQGIVDG6qG0wUDytk9o-fCPhFdG51_cdUp7u8R9b_hwGMfSVSUMQZ1YdU5lRsXbX$>

From: Eric Rieve <[email protected]<mailto:[email protected]>>
Sent: Wednesday, April 5, 2023 8:44 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: [EXTERNAL] Re: Standpipes & FDC

This makes me pretty leery. If the manual dry standpipe isn’t studiously 
inspected for open valves or broken pipes then when the FDC is charged you 
could have a huge inadvertent discharge into the manual system and potentially 
not be able to provide needed fire flow for the wet standpipes.

I’d say you’d either need two separate FDCs, or if you go with just a single 
one then the manual dry standpipe would need a control valve that was 
immediately accessible to the Fire Dept to close off the manual standpipe if 
the above event occurs.

Honestly I’d go with two FDC’s and just make sure you hang really good signage 
stating what systems they feed.

Hope this helps.

Eric Rieve
Rieve Fire Protection

From: Kyle.Montgomery 
<[email protected]<mailto:[email protected]>>
Sent: Wednesday, April 5, 2023 11:12 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: [EXTERNAL] Re: Standpipes & FDC

What if there was a check valve separating the wet from the dry, and the FDC 
was connected to the dry side?

-Kyle M

From: Craig Hanson <[email protected]<mailto:[email protected]>>
Sent: Wednesday, April 5, 2023 7:15 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [EXTERNAL] [Sprinklerforum] Re: Standpipes & FDC

Brian,

I agree with Travis. If you have a true dry manual then it is not connected to 
other systems. If you have a dry automatic then it will have its own dry pipe 
valve and then could be connected to the FDC through the common manifold.



Craig D. Hanson, CFPS
Senior Fire Plans Examiner
West Coast Code Consultants, Inc. (WC³)
Meridian Satellite Office
C: 253.225.9977 | E: [email protected]<mailto:[email protected]> | 
www.WC-3.com<https://urldefense.com/v3/__https:/www.wc-3.com/__;!!Ba8_KKAT!JgEEuYYWcSGA9xERaPxkutYVaGZxzf1A3NGmorhlsRo-33V2-AFsTha0CPwYx2SjZUEdukTfjzsPXF8_pA$>
Teaming With Your Community to Make a Difference


On Wed, Apr 5, 2023 at 8:12 AM Brian Harris 
<[email protected]<mailto:[email protected]>> wrote:
Travis-
Great question. It’s not a job we’re working on so I don’t know the specifics, 
the question was just brought up in the office.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<https://urldefense.com/v3/__http:/bvssystemsinc.com/__;!!Ba8_KKAT!JgEEuYYWcSGA9xERaPxkutYVaGZxzf1A3NGmorhlsRo-33V2-AFsTha0CPwYx2SjZUEdukTfjzvi_0m_3A$>


From: Travis Mack <[email protected]<mailto:[email protected]>>
Sent: Wednesday, April 05, 2023 10:10 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Standpipes & FDC

Yes they can, provided it is arranged correctly.  But how are you having manual 
and wet standpipes in the same building?


Travis Mack, SET
M.E.P.CAD |
181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074
www.mepcad.com<https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=http*3a*2f*2fwww.mepcad.com*2f&c=E,1,_5vJCgAl4QFHzkIIRkd9oYRYUw-ncaw2oaIpcjXfGNJ47LRTSszKbPVSY3xCtulufqJGZG3nE6qXPE4yrhDZCf0VSbfBO5dWBI2o0-pzhLUCjOSZ5nYxnaYeYBL6&typo=1__;JSUlJQ!!Ba8_KKAT!JgEEuYYWcSGA9xERaPxkutYVaGZxzf1A3NGmorhlsRo-33V2-AFsTha0CPwYx2SjZUEdukTfjzufa4SN0A$>
 | m: 480.547.9348

AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD

Book appointment time in my calendar
https://calendly.com/t_mack_mepcad<https://urldefense.com/v3/__https:/calendly.com/t_mack_mepcad__;!!Ba8_KKAT!JgEEuYYWcSGA9xERaPxkutYVaGZxzf1A3NGmorhlsRo-33V2-AFsTha0CPwYx2SjZUEdukTfjzuL1RPfJA$>

From: Brian Harris <[email protected]<mailto:[email protected]>>
Sent: Wednesday, April 5, 2023 7:06 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [Sprinklerforum] Standpipes & FDC

Quick question:
A parking garage has (3) standpipes. 2 are wet automatic (conditioned space) & 
1 is manual dry. Can they all be fed from one FDC?

Brian Harris, CET
BVS Systems Inc.
bvssystemsinc.com<https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=http*3a*2f*2fbvssystemsinc.com*2f&c=E,1,v1ImuXOodSkbLZC67sTeOVl5n25H7NmStHDkMra-WquXnTKQq5SGcQODBnzkfkanf-3E_swdaJZ0VcTno0eEVAtJ8mC-Yc0w1ThKRhzkkk3Mog,,&typo=1__;JSUlJQ!!Ba8_KKAT!JgEEuYYWcSGA9xERaPxkutYVaGZxzf1A3NGmorhlsRo-33V2-AFsTha0CPwYx2SjZUEdukTfjzuMtna0lg$>
Phone: 704.896.9989
Fax: 704.896.1935



_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.com/v3/__https:/lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org__;!!Ba8_KKAT!JgEEuYYWcSGA9xERaPxkutYVaGZxzf1A3NGmorhlsRo-33V2-AFsTha0CPwYx2SjZUEdukTfjzvjUo46mQ$>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to