Man, y’all are going off in all different directions.   As best as I can see, 
there are two areas of query here that aren’t actually congruent.

If the subject has areas that are conditioned, then a wet standpipe must be 
installed.   Areas subject to freezing shall be dry.   Doesn’t matter if they 
are manual, automatic or semi-automatic, just wet or dry depending on 
subjectivity to freezing.   (Yes to Travis’s comment below, supervisory air is 
now required for all dry standpipes.)

What I’m wondering is why the initial what-if is based on automatic-wet and 
manual dry?  Is this a high-rise building?   If not, why make the wet system 
automatic?   Once that’s resolved then…

FDC (or FDC’s) can be arranged so that you pump both wet and dry, but if you do 
then the dry side has to be properly drained and restored to its 
driest-possible condition.    Which may if fact be the best arrangement because 
the fire department will otherwise have to sort through multiple FDC’s.   Now 
to me, that’s not too big of a challenge because all you need is love (signage, 
actually).    But if this building experiences a fire and both wet-f and 
dry-served common floors, then you’re going to want an active water supply in 
ALL standpipes so the 1st team in can pick whatever stair they recon as the 
best one to use on the fire floor.

So like many subjective standpipe questions, this goes back to the responding 
FD’s preferences and attack strategies for buildings equipped with standpipes.  
 Pick an arrangement that is the best assimilation of value and reliability and 
propose it to them for consideration.

The foregoing is my opinion only and does not represent NFPA or the NFPA 14 
Technical Committee, nor intended to serve as an interpretation of the standard.

Protection Design and Consulting
Steve Leyton, President
T  |  619.255.8964 x 102  |  
www.protectiondesign.com<http://www.protectiondesign.com/>
2851 Camino Del Rio South  |  Suite 210  |  San Diego, CA  92108
Fire Protection System Design | Consulting | Planning | Training





pumping all st

From: Travis Mack <[email protected]>
Sent: Wednesday, April 05, 2023 9:01 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: [EXTERNAL] Re: Standpipes & FDC

That is from NFPA 14, 2019 edition.  Check the 2016 edition.  It’s there as 
well.


Travis Mack, SET
M.E.P.CAD |
181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074
www.mepcad.com<http://www.mepcad.com/> | m: 480.547.9348

AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD

Book appointment time in my calendar
https://calendly.com/t_mack_mepcad

From: Prahl, Craig <[email protected]<mailto:[email protected]>>
Sent: Wednesday, April 5, 2023 8:59 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: [EXTERNAL] Re: Standpipes & FDC

Travis, what standard or code are you referencing?

I would question the requirement of providing supervisory air in a manual 
standpipe based on the language of 6.1.1 specifically addressing Dry 
standpipes.  A dry standpipe and a Manual standpipe are distinctly different.

Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$>
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS


From: Travis Mack <[email protected]<mailto:[email protected]>>
Sent: Wednesday, April 5, 2023 11:49 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: [EXTERNAL] Re: Standpipes & FDC

All dry standpipes,  including manual standpipes, are required to have 
supervisory air to help protect against that situation described.  This was 
added, I believe, in the 2016 edition.  This is a snip from the 2019 edition.

6.1.1 Location of Dry Standpipes.
Dry standpipes shall be monitored in accordance with NFPA 72 with supervisory 
air pressure.
ENHANCED CONTENT
Collapse
Standpipe systems, including standalone manual standpipes, need to be 
supervised to ensure proper operation and integrity of the system. Supervision 
can be achieved through central station, a constantly attended local station, 
or by a signal or local alarm at the initiating device attached to the 
standpipe system.




Travis Mack, SET
M.E.P.CAD |
181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074
www.mepcad.com<https://urldefense.com/v3/__http:/www.mepcad.com/__;!!B5cixuoO7ltTeg!FsG36-XDvOQrgI_DHQGIVDG6qG0wUDytk9o-fCPhFdG51_cdUp7u8R9b_hwGMfSVSUMQZ1YdU_uNHp9p$>
 | m: 480.547.9348

AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD

Book appointment time in my calendar
https://calendly.com/t_mack_mepcad<https://urldefense.com/v3/__https:/calendly.com/t_mack_mepcad__;!!B5cixuoO7ltTeg!FsG36-XDvOQrgI_DHQGIVDG6qG0wUDytk9o-fCPhFdG51_cdUp7u8R9b_hwGMfSVSUMQZ1YdU5lRsXbX$>

From: Eric Rieve <[email protected]<mailto:[email protected]>>
Sent: Wednesday, April 5, 2023 8:44 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: [EXTERNAL] Re: Standpipes & FDC

This makes me pretty leery. If the manual dry standpipe isn’t studiously 
inspected for open valves or broken pipes then when the FDC is charged you 
could have a huge inadvertent discharge into the manual system and potentially 
not be able to provide needed fire flow for the wet standpipes.

I’d say you’d either need two separate FDCs, or if you go with just a single 
one then the manual dry standpipe would need a control valve that was 
immediately accessible to the Fire Dept to close off the manual standpipe if 
the above event occurs.

Honestly I’d go with two FDC’s and just make sure you hang really good signage 
stating what systems they feed.

Hope this helps.

Eric Rieve
Rieve Fire Protection

From: Kyle.Montgomery 
<[email protected]<mailto:[email protected]>>
Sent: Wednesday, April 5, 2023 11:12 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: [EXTERNAL] Re: Standpipes & FDC

What if there was a check valve separating the wet from the dry, and the FDC 
was connected to the dry side?

-Kyle M

From: Craig Hanson <[email protected]<mailto:[email protected]>>
Sent: Wednesday, April 5, 2023 7:15 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [EXTERNAL] [Sprinklerforum] Re: Standpipes & FDC

Brian,

I agree with Travis. If you have a true dry manual then it is not connected to 
other systems. If you have a dry automatic then it will have its own dry pipe 
valve and then could be connected to the FDC through the common manifold.



Craig D. Hanson, CFPS
Senior Fire Plans Examiner
West Coast Code Consultants, Inc. (WC³)
Meridian Satellite Office
C: 253.225.9977 | E: [email protected]<mailto:[email protected]> | 
www.WC-3.com<https://urldefense.com/v3/__https:/www.wc-3.com/__;!!Ba8_KKAT!JgEEuYYWcSGA9xERaPxkutYVaGZxzf1A3NGmorhlsRo-33V2-AFsTha0CPwYx2SjZUEdukTfjzsPXF8_pA$>
Teaming With Your Community to Make a Difference


On Wed, Apr 5, 2023 at 8:12 AM Brian Harris 
<[email protected]<mailto:[email protected]>> wrote:
Travis-
Great question. It’s not a job we’re working on so I don’t know the specifics, 
the question was just brought up in the office.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<https://urldefense.com/v3/__http:/bvssystemsinc.com/__;!!Ba8_KKAT!JgEEuYYWcSGA9xERaPxkutYVaGZxzf1A3NGmorhlsRo-33V2-AFsTha0CPwYx2SjZUEdukTfjzvi_0m_3A$>


From: Travis Mack <[email protected]<mailto:[email protected]>>
Sent: Wednesday, April 05, 2023 10:10 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Standpipes & FDC

Yes they can, provided it is arranged correctly.  But how are you having manual 
and wet standpipes in the same building?


Travis Mack, SET
M.E.P.CAD |
181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074
www.mepcad.com<https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=http*3a*2f*2fwww.mepcad.com*2f&c=E,1,_5vJCgAl4QFHzkIIRkd9oYRYUw-ncaw2oaIpcjXfGNJ47LRTSszKbPVSY3xCtulufqJGZG3nE6qXPE4yrhDZCf0VSbfBO5dWBI2o0-pzhLUCjOSZ5nYxnaYeYBL6&typo=1__;JSUlJQ!!Ba8_KKAT!JgEEuYYWcSGA9xERaPxkutYVaGZxzf1A3NGmorhlsRo-33V2-AFsTha0CPwYx2SjZUEdukTfjzufa4SN0A$>
 | m: 480.547.9348

AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD

Book appointment time in my calendar
https://calendly.com/t_mack_mepcad<https://urldefense.com/v3/__https:/calendly.com/t_mack_mepcad__;!!Ba8_KKAT!JgEEuYYWcSGA9xERaPxkutYVaGZxzf1A3NGmorhlsRo-33V2-AFsTha0CPwYx2SjZUEdukTfjzuL1RPfJA$>

From: Brian Harris <[email protected]<mailto:[email protected]>>
Sent: Wednesday, April 5, 2023 7:06 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [Sprinklerforum] Standpipes & FDC

Quick question:
A parking garage has (3) standpipes. 2 are wet automatic (conditioned space) & 
1 is manual dry. Can they all be fed from one FDC?

Brian Harris, CET
BVS Systems Inc.
bvssystemsinc.com<https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=http*3a*2f*2fbvssystemsinc.com*2f&c=E,1,v1ImuXOodSkbLZC67sTeOVl5n25H7NmStHDkMra-WquXnTKQq5SGcQODBnzkfkanf-3E_swdaJZ0VcTno0eEVAtJ8mC-Yc0w1ThKRhzkkk3Mog,,&typo=1__;JSUlJQ!!Ba8_KKAT!JgEEuYYWcSGA9xERaPxkutYVaGZxzf1A3NGmorhlsRo-33V2-AFsTha0CPwYx2SjZUEdukTfjzuMtna0lg$>
Phone: 704.896.9989
Fax: 704.896.1935



_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.com/v3/__https:/lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org__;!!Ba8_KKAT!JgEEuYYWcSGA9xERaPxkutYVaGZxzf1A3NGmorhlsRo-33V2-AFsTha0CPwYx2SjZUEdukTfjzvjUo46mQ$>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to