If your main concern is the temperature note the term “nominal” which means 
“stated or expressed but not necessarily corresponding exactly to the real 
value”.  Typically you’d see heads ranging from 155-165 depending on design 
that would all be considered interchangeable for the purposes of that 
requirement.  23.4.4 refers to ceiling sprinklers for a particular application. 
 If FM is your primary concern they make no differentiation between “ESFR” and 
other storage type heads, they’re only concerned with the orifice size/k factor 
of the head.

Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive • Fort Wayne, IN • 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]
[cid:[email protected]]

From: Phong - Indochine Engineering <[email protected]>
Sent: Tuesday, April 18, 2023 3:12 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] FM approved in-rack sprinkler head

Dear All, I am having a problem when choosing in-rack sprinkler head with FM 
approved, and having the right temperature. As per FM Global Property Loss 
Prevention Data Sheets 8-9, March 2010 Interim Revision July 2021, 2. 3. 4. 3 
K-Factors, Nominal
ZjQcmQRYFpfptBannerStart
Be Careful With This Message
The sender's identity could not be verified and someone may be impersonating 
the sender.
ZjQcmQRYFpfptBannerEnd
Dear All,

I am having a problem when choosing in-rack sprinkler head with FM approved, 
and having the right temperature.

As per FM Global Property Loss Prevention Data Sheets 8-9, March 2010
Interim Revision July 2021,

2.3.4.3<https://urldefense.com/v3/__http:/2.3.4.3__;!!FaxH778!a8wz2QX3Ov8SR-NPmTRkFZcm58VeyggKZ0CIB86Qyp763XR5-fEHk36tmRoLBVct5vf1h4Msac--Nzc$>
 K-Factors, Nominal Temperature Rating, and RTI Rating of In-Rack Storage 
Sprinklers
2.3.4.3.1 Use nominally rated 160°F (70°C) FM Approved in-rack sprinklers for 
all in-rack sprinkler
installations.

I cannot find actual sprinkler head approved by FM and having this rated 160°F 
(70°C), for example, this model of Viking (bulb type)

https://www.approvalguide.com/productDetail?productid=118279<https://urldefense.com/v3/__https:/www.approvalguide.com/productDetail?productid=118279__;!!FaxH778!a8wz2QX3Ov8SR-NPmTRkFZcm58VeyggKZ0CIB86Qyp763XR5-fEHk36tmRoLBVct5vf1h4MsiX-Sy8M$>

Should I follow NFPA13,
Chapter 23 - ESFR Requirements for Storage Applications
23.4.4 Sprinklers shall be intermediate temperature–rated ESFR pendent 
sprinklers with a nominal K-factor of K-25.2 (360).

Checking the Viking ESFR sprinkler head, it seems only the fusible type is 
ranked as ESFR:
Early Suppression Fast Response (ESFR) | Viking Group 
Inc.<https://urldefense.com/v3/__https:/www.vikinggroupinc.com/products/viking-fire-sprinklers/storage/esfr-early-suppression-fast-response-sprinklers__;!!FaxH778!a8wz2QX3Ov8SR-NPmTRkFZcm58VeyggKZ0CIB86Qyp763XR5-fEHk36tmRoLBVct5vf1h4MsP3TUGws$>

But the temperature of Viking ESFR sprinkler head having FM approved is also 
not rated 160°F (70°C), but 74°C and 96°C
FM3007275.PDF 
(vikinggroupinc.com)<https://urldefense.com/v3/__https:/www.vikinggroupinc.com/sites/default/files/databook/sprinklers/storage/121aefm.pdf__;!!FaxH778!a8wz2QX3Ov8SR-NPmTRkFZcm58VeyggKZ0CIB86Qyp763XR5-fEHk36tmRoLBVct5vf1h4MsDcx_6Hg$>

Please can you advise.

Regards,
Le Vu Phong

[cid:[email protected]]

Indochine Engineering Vietnam JSC
Unit 12-01
Pearl Plaza
561A Dien Bien Phu Street
Binh Thanh District, HCMC, VN

Mobile:  +84 (0) 902 363 525
Tel:  +84 (8) 3512 4100
Fax: +84 (8) 3512 4108

Web: 
www.indoeng.com<https://urldefense.com/v3/__http:/www.indoeng.com/__;!!FaxH778!a8wz2QX3Ov8SR-NPmTRkFZcm58VeyggKZ0CIB86Qyp763XR5-fEHk36tmRoLBVct5vf1h4Msnp4sqmE$>

[cid:[email protected]]<https://urldefense.com/v3/__http:/www.linkedin.com/company/2077231__;!!FaxH778!a8wz2QX3Ov8SR-NPmTRkFZcm58VeyggKZ0CIB86Qyp763XR5-fEHk36tmRoLBVct5vf1h4Mshy0kobw$>
[cid:[email protected]]<https://urldefense.com/v3/__http:/www.twitter.com/indoeng___;!!FaxH778!a8wz2QX3Ov8SR-NPmTRkFZcm58VeyggKZ0CIB86Qyp763XR5-fEHk36tmRoLBVct5vf1h4Ms17m-yKQ$>
[cid:[email protected]]<https://urldefense.com/v3/__http:/www.youtube.com/user/indochineengineering__;!!FaxH778!a8wz2QX3Ov8SR-NPmTRkFZcm58VeyggKZ0CIB86Qyp763XR5-fEHk36tmRoLBVct5vf1h4Ms9h8s0Yk$>
[cid:[email protected]]
phong_indochineengineering



This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to