One of the things that I see, living in an area with 80+ year old systems, is 
that the newer inspectors are asking for calc signs on pipe schedule systems. 
Hydraulically calculating    pipe schedule system can be a disaster. They are 2 
separate and individual system designs. A system may not necessarily meet both 
sets of criteria.   
  

  
A good example is a school in my town that has a pipe schedule system installed 
in the 1950s. I was asked to do a hydraulic calculation. The 2535 sqft design 
area in the attic contained 54 sprinklers. No way that calc was going to work.  
 
  

  
We probably should be labeling pipe schedule systems as such.   
  
  
  
  
Todd Williams     

  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-608-4559
  
  
  
  
  

  
  
>   
> On Jul 30, 2024 at 10:56 AM,  <Ken Wagoner 
> (mailto:[email protected])>  wrote:
>   
>   
>   There is certainly an issue on that missing information.    NFPA 25 
> addresses the need for this sign/information in ยง5.2.5 (2023 ed). And some of 
> the "enhanced content" on NFPA Link to this section that this is to be noted 
> as a "deficiency", although it is a "noncritical" deficiency as it doesn't 
> impair the ability of the system to function in a fire.
>   
>  I've done considerable work on existing buildings which were being 
> repurposed from a factory to storage, and without this information the costs 
> of the revisions went way up since a retro set of calculations had to be 
> performed.
>   
>  just my thoughts,
>   
> Ken Wagoner, SET
>   Parsley Consulting
>  500 West Mechanic Street
>  Harrisonville, Missouri 64701-2235
>   Phone: (760) 745-6181
>    Visit the website 
> (https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1)
>    
>
>   
>
>
>   
>  _________________________________________________________ SprinklerForum 
> mailing list: 
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> To unsubscribe send an email to [email protected]
>   
  
  
     
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to