Not sure, but maybe check out NFPA 13 2022 25.1.4..2 – In-Rack Sprinkler System 
Control Valves.

Thanks,
Gregg Fontes
Lead Estimator
O: 209-334-9119
[email protected]<mailto:[email protected]>

[image001.jpg]

This and any attached documents are for the use of the intended recipient(s) 
only and may contain information that is privileged, confidential, or work 
product that may be exempt from disclosure under applicable law. If you are not 
the intended recipient, any use, dissemination, distribution, or copying of 
this communication and any attachments is strictly prohibited, and you are 
hereby requested to delete this message and any attached documents, to destroy 
any printed copies, and to telephone or otherwise contact the sender 
immediately about the error

From: Brett Peters <[email protected]>
Sent: Tuesday, August 13, 2024 6:36 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: In-Rack system connected to an adjacent system

25.1.3.2* In-Rack Sprinkler System Control Valves.
A.25.1.3.2 In-rack sprinklers and ceiling sprinklers selected for protection 
should be controlled
by at least two separate indicating valves and drains. In higher rack 
arrangements,
consideration should be given to providing more than one in-rack control valve 
to limit the
extent of any single impairment.
The control valves addressed in 25.1.3.2 are intended to allow isolation of the 
in-rack system from the ceiling
system, as indicated in Exhibit 25.1. In-rack sprinklers are susceptible to 
damage due to their location.
Control valves are required to allow the ceiling system to remain in service 
while an in-rack sprinkler is
replaced. Additionally, when the ceiling system is out of service, the valves 
are to be arranged so that the
in-rack system remains operational.
25.1.3.2.1 Unless the requirements of 25.1.3.2.2 or 25.1.3.2.3 are met, 
separate indicating
control valves and drains shall be provided and arranged so that ceiling and 
in-rack sprinkler
systems can be controlled independently.
Sprinklers and sprinkler piping installed in pallet racks are more likely to 
experience damage from forklifts
or other material-handling equipment. Providing a separate control valve allows 
the piping to be shut
down quickly without impairing ceiling-level protection for the entire area of 
the building.


I will be away from the office on Friday August 16th and will have limited 
access to phone and email.


Thanks



Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
[email protected]<mailto:[email protected]>
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718 2676 24h
Visit us at www.proudline.ca<http://www.proudline.ca/>

Proudline now offers ULc listed monitoring services, please contact 
[email protected]<mailto:[email protected]> for more information



[https://ci3.googleusercontent.com/mail-sig/AIorK4wRo6r0eNDUWx8YR-4XJLvwcnouQn_xEZH_HIb4jDbepWtON2RWC-ekzvZHKtncFOQqPcNQfzM]
 
[https://ci3.googleusercontent.com/mail-sig/AIorK4yJVI287VPLDWiW9maE2Np3U4CdszCY9deeyaLl8DM90wlBd7pnuOZV9U-swv-7gWN_24py6vo]
  
[https://ci3.googleusercontent.com/mail-sig/AIorK4wlGmqj6Ja06DKOIMLPvEE8B2W8fT_TPPA3w-4JfqygLq9n77ECSni09YLIVICXJYzWo4Z0PjU]
  
[https://ci3.googleusercontent.com/mail-sig/AIorK4zEgPbs279KVEfWIpIiWNLel8zAlcloW9dNXGLTaE1cMz88CRkmg17fju5BQB_iIzhWK20DUL8]
  
[https://ci3.googleusercontent.com/mail-sig/AIorK4z7J0kfmSGA8jKvDK0pTqW3KQlc5v-tYcWosmy5W7pdok462Gzu_9Ft7UK9oJUWDT1DzhQ4hUU]
  
[https://ci3.googleusercontent.com/mail-sig/AIorK4wTVHoTZxkppBoWSCTFnGLgGTq0apivi8sNvWPyBsloO0mmy8ZYu4Ax854jo7ihTMFyeYeOceg]
  
[https://ci3.googleusercontent.com/mail-sig/AIorK4xwBWEOX5v9mpza4Jqf9lOKSwThBNvyIO7Rl-Cxo7NRiV7p70C0f1biwbh44Y-iIA5GcmD1MCo]
  
[https://ci3.googleusercontent.com/mail-sig/AIorK4yPfO1HdtbQPYiKlYE38cwc88ABhX7xN1nh0fCK5LjFXjKplJggk3Xn6_XypmtMWyADKR7ZRGk]


On Mon, Aug 12, 2024 at 5:25 PM Hinson, Ryan 
<[email protected]<mailto:[email protected]>> wrote:
Not exactly what you are looking for but take a peak at NFPA 13 (2022) Section 
19.3.3.3 regarding water curtains.  As long as you include, and balance, the 
additional demand in your calculations, it is my opinion that you should be 
fine.

I recall back in the day we used to do this. I looked in NFPA 13 (2007) Section 
22.8 and found the following:

               22.8 In-Rack Sprinklers.

22.8.1 Pipes to in-rack sprinklers shall be sized by hydraulic calculations.
22.8.2 Water demand of sprinklers installed in racks shall be added to ceiling 
sprinkler water demand over the same protected area at the point of connection.

22.8.3 The demand shall be balanced to the higher pressure.

22.8.4 Water demand of sprinklers installed in racks or water curtains shall be 
added to the ceiling sprinkler water demand at the point of connection. Demands 
shall be balanced to the higher pressure. (See Chapter 8.)

I believe the reference to Chapter 8 was incorrect and should have instead been 
to Chapter 11.

Hope this helps,

Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell
Associate Fire Protection Engineer \ Upper Midwest Region
O 612-900-3755 \  M 763-688-4045 \  F 952-229-2923
[email protected]<mailto:[email protected]>  \  
burnsmcd.com<http://www.burnsmcd.com/>
8201 Norman Center Drive, Suite 500  \  Bloomington, MN 55437
*Registered in: AK, LA, MD, MN, PA, TX, & UT
**NICET IV - Water-Based Systems Layout

From: James Crawford <[email protected]<mailto:[email protected]>>
Sent: Monday, August 12, 2024 5:26 PM
To: 
[email protected]<mailto:[email protected]>
Subject: [Sprinklerforum] In-Rack system connected to an adjacent system

A question has been asked in our office regarding connecting an in-rack system 
into an adjacent roof system.

It is in a multi-tenant building that has multiple roof zones, the system only 
has 11 heads but does not work when connected into the roof system in that 
tenant space.

Option is to run 500 feet back to the valve room or connect into an adjacent 
roof system.

We can not find anything that says you can’t but cannot find anything that says 
you can.

My concern would be monitoring of the zones, so you would have multiple zones 
going off if there was a fire.

Comments:

Thank You

James Crawford
Phaser Fire Protection Ltd.
Phone 604-888-0318
Cel: 604-790-0938
Email [email protected]<mailto:[email protected]>
Web: www.phaserfire.ca<http://www.phaserfire.ca/>


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to