Taylor,

I don't think you'll find one, and also don't think the head underneath a 
garage door would need to be the same temp as the ceiling sprinklers.

I don't think there is an exact code reference for this in the current edition 
of 13. The next edition of NFPA-13 will state(at least per what is shown on the 
2nd draft report) that supplemental sprinklers will need to be QR and have an 
ordinary temp rating unless the specific location requires a higher temperature 
per 9.4.2.5.

Hope this helps!
Eric, Rieve, SE
Rieve Fire Protection

From: Taylor Schumacher <[email protected]>
Sent: Tuesday, August 13, 2024 12:19 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] ECLH High Temp Sidewall

Does anyone know of an ECLH High Temp Sidewall?

Maybe I'm overthinking trying to match the overhead temperature under a garage 
door...


Taylor Schumacher