From: Eric Rieve <[email protected]> Sent: Tuesday, August 13, 2024 12:59 PM To: Discussion list on issues relating to automatic fire sprinklers <[email protected]> Subject: [Sprinklerforum] Re: ECLH High Temp Sidewall Caution: This email originated from outside your organization. Please take care when clicking links or opening attachments. Taylor, I don't think you'll find one, and also don't think the head underneath a garage door would need to be the same temp as the ceiling sprinklers. I don't think there is an exact code reference for this in the current edition of 13. The next edition of NFPA-13 will state(at least per what is shown on the 2nd draft report) that supplemental sprinklers will need to be QR and have an ordinary temp rating unless the specific location requires a higher temperature per 9.4.2.5. Hope this helps! Eric, Rieve, SE Rieve Fire Protection From: Taylor Schumacher <[email protected]<mailto:[email protected]>> Sent: Tuesday, August 13, 2024 12:19 PM To: Discussion list on issues relating to automatic fire sprinklers <[email protected]<mailto:[email protected]>> Subject: [Sprinklerforum] ECLH High Temp Sidewall Does anyone know of an ECLH High Temp Sidewall? Maybe I'm overthinking trying to match the overhead temperature under a garage door... Taylor Schumacher