We have a customer that wants to change the existing antifreeze to a dry 
system.  All the sprinklers on the system are pendents on drops.  It is a pipe 
schedule system.  I think the best way to do this is keep the existing piping, 
change the sprinklers and verify the pipe is pitched correctly to drain as 
required or add low point drains if needed.  This way the sprinklers line up 
with existing holes from the attic.  The building is an independent living 
building (light hazard/residential).  My questions are 1) does the system need 
to be calculated since it's a pipe schedule and 2) If so, can we use the room 
design method on a dry system?  We are on the 2019 edition of NFPA 13.  I did 
not see anything in chapter 19 on using room design for dry systems and don't 
recall ever seeing that.  With that in mind, if we calculate the 1950 sq. ft., 
there are a lot of closets included in that that kill the calculations. 
  The building was built in 1999, of course no drawings and the pipe looks as 
good as new inside and out.
Jay Stough 
Tustin Fire Solutions 