If the dry system is protecting dwelling units you need to meet 15 seconds
for water delivery time.


Benjamin Young


On Thu, Apr 3, 2025 at 7:26 AM Jay Google <jaycs7...@gmail.com> wrote:

> We have a customer that wants to change the existing antifreeze to a dry
> system.  All the sprinklers on the system are pendents on drops.  It is a
> pipe schedule system.  I think the best way to do this is keep the existing
> piping, change the sprinklers and verify the pipe is pitched correctly to
> drain as required or add low point drains if needed.  This way the
> sprinklers line up with existing holes from the attic.  The building is an
> independent living building (light hazard/residential).  My questions are
> 1) does the system need to be calculated since it's a pipe schedule and 2)
> If so, can we use the room design method on a dry system?  We are on the
> 2019 edition of NFPA 13.  I did not see anything in chapter 19 on using
> room design for dry systems and don't recall ever seeing that.  With that
> in mind, if we calculate the 1950 sq. ft., there are a lot of closets
> included in that that kill the calculations.
>   The building was built in 1999, of course no drawings and the pipe looks
> as good as new inside and out.
>
> *Jay Stough*
>
> *Tustin Fire Solutions *
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> sprinklerforum-le...@lists.firesprinkler.org
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to