Ok this is a new one for me. Have a diesel driven fire pump that has a PLD 
pressure limiting driver. When it comes to the annual flow test, how do I test 
this properly per Nfpa? Would this be tested as a variable speed pump per nfpa?
I know on start up you disable the PLD to test and set relief valve pressure. 
On annual flow test the net pressure is low because RPMs are limited. Do I 
disable the PLD for the test to compare with pump data plate?  OR use RPM 
correction formula with PLD on? OR test as a variable speed pump? Sorry first 
PLD pump for me this is cool stuff just want to make sure I test it right. Not 
finding much info on PLD PUMPS 8n nfpa.

Ps called the manufacturer they could not help with annual testing requirements.