Assumption: all spaces where pipe and sprinklers are located will be heated.   
  

  
There is nothing that says you can’t (that I am aware of). However, you will 
need to maintain the “U-loop” shape as you would with hard pipe.   
  
  
  
  
Todd Williams     

  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-608-4559
  
  
  
  
  

  
  
>   
> On Oct 28, 2025 at 9:13 AM,  <Taylor Schumacher 
> (mailto:[email protected])>  wrote:
>   
>   
>       
>   
>
> I have a dry system that is feeding upright sprinklers on sprigs in a  heated 
>  light hazard space. The owner wants to add ACT. I’m wondering if I can use 
> flex drops into the ACT. Feels weird, but I cannot find any reason why I 
> shouldn’t.
>
>   
>
>   
>
>   
>