Related to this, I have a dry system I’m reviewing that features return
beds feeding a dry pendant head.  My argument is that the environment is
not maintained at 40F or above as mentioned in the 2016 edition section
7.2.2.  I see water filling the return bend during a three year full trip.
His argument is that he is using a listed dry sprinkler. Who is right?

Zach

On Wed, Oct 29, 2025 at 1:13 PM John Denhardt <[email protected]>
wrote:

> While fully allowed, having piping containing water in a dry pipe system
> most likely will lead to accelerated corrosion of the dry pipe piping
> system.
>
> *Thanks,*
>
> *John*
>
> *John August Denhardt, P.E*
> Vice President Engineering and Technical Services
> American Fire Sprinkler Association
> 301-343-1457
>
> *Are you a member with a technical question? *
>
> Don't forget one of the most valuable resources that AFSA provides is
> Technical Reviews by our Technical Services Department. It’s like having an
> FPE on your staff. Visit www.firesprinkler.org/technicalreview to submit
> a question today! (Member login required.)
>
> On Oct 29, 2025, at 12:59, Taylor Schumacher <[email protected]>
> wrote:
>
> 
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
> I have a dry system that is feeding upright sprinklers on sprigs in a
> *heated* light hazard space. The owner wants to add ACT. I’m wondering if
> I can use flex drops into the ACT. Feels weird, but I cannot find any
> reason why I shouldn’t.
>
>
>
> *Taylor Schumacher*
>
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to