Ceiling over 55’ your only real option is in racks.  Only issue is how you sell 
sprinkling the shell unless you just call it low pile storage and do a hazard 
group design.  Since you technically can’t put an ESFR design in and call it 
acceptable without the “virtual floor” of scheme A once the racks are in.


Mike Morey

CFPS 3229 • NICET S.E.T. 123677

Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company

7614 Opportunity Drive • Fort Wayne, IN • 46825

direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]

[Image]

________________________________
From: Greg Held <[email protected]>
Sent: Thursday, November 27, 2025 2:33:55 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Design for buildings greater than 50ft

Unfortunately, the ceiling is higher than 55ft From: Brett Peters <brett@ 
proudline. ca> Sent: Thursday, November 27, 2025 11: 31: 18 AM To: Discussion 
list on issues relating to automatic fire sprinklers <sprinklerforum@ lists. 
firesprinkler. org>
ZjQcmQRYFpfptBannerStart
This Message Is From an Untrusted Sender
You have not previously corresponded with this sender.

ZjQcmQRYFpfptBannerEnd
Unfortunately, the ceiling is higher than 55ft

________________________________
From: Brett Peters <[email protected]>
Sent: Thursday, November 27, 2025 11:31:18 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Design for buildings greater than 50ft

The Tyco ESFR34 is designed for 50'-0 of storage with maximum ceiling height of 
55'-0 and I think the Reliable M336 is the same

I don't know of any other sprinklers that will go that high or higher. The only 
other protection schemes I am aware of include providing ESFR in rack 
sprinklers (ESFR in racks can be placed with larger height intervals than 
traditional in rack sprinklers)




Thanks

Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
[email protected]<mailto:[email protected]>
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718 2676 24h
Visit us at 
www.proudline.ca<https://urldefense.com/v3/__https://linkprotect.cudasvc.com/url?a=http*3a*2f*2fwww.proudline.ca*2f&c=E,1,IIB6fBvb4dpIffFjJBKjmfGYZ5Zf0vgRULiUlKZUyeSjUEtwP4FlolZt7kjDDZAqSFXMho1wOlUTSErKzDWV6dyrLrfqsYJ-5NYcmUgaPQT-&typo=1__;JSUlJQ!!FaxH778!aqlEnecQGHKgLBtlqiH-zwJML521Ca91RuxZ6cKDLhbusSC-2uzEAhs-0m2Dgp9kOr15roxWdHkemN19$>


On Thu, Nov 27, 2025 at 12:00 PM Greg Held 
<[email protected]<mailto:[email protected]>> wrote:
I am curious if anyone can direct me on how to design ceiling only protection 
for a building with a roof greater than 50ft.  The building will eventually 
have storage, but there is no information about the racking at this time.  What 
is known is that it will have Class I-IV commodities.

Thank you,


Greg Held

[email protected]<mailto:[email protected]>

Delta Fire, Inc.



[cid:ii_19ac6c76c476cb2bff1]





14795 SW 72nd Avenue

Portland, Oregon 97224

503.620.4020 X 113

www.deltafire.com<https://urldefense.com/v3/__https://linkprotect.cudasvc.com/url?a=https*3a*2f*2fna01.safelinks.protection.outlook.com*2f*3furl*3dwww.deltafire.com*26data*3d02*257C01*257Ckathy.marino*2540am.jll.com*257C600ab234ae2d4d2b00c508d678109cba*257Cbfef2b06d2564f8ebd038d3687987063*257C0*257C0*257C636828410093238795*26sdata*3dx1*252BYPL61aI20rvrTQFvlKeMIhihsy6Nl1iA09WKzy*252Bo*253D*26reserved*3d0&c=E,1,rb7C4lGy0hyBGI8mYFNvU2fvf-9s8Ixcp5bxlrEKKBpxoQl_mpaMrDN-rQKKzIxisb640B165slEuNBsxrlk8ocq3KWm7C0AZUlsuHWd2Q,,&typo=1__;JSUlJSUlJSUlJSUlJSUlJSUlJSUlJSU!!FaxH778!aqlEnecQGHKgLBtlqiH-zwJML521Ca91RuxZ6cKDLhbusSC-2uzEAhs-0m2Dgp9kOr15roxWdEJleblf$>


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.com/v3/__https://linkprotect.cudasvc.com/url?a=https*3a*2f*2flists.firesprinkler.org*2flist*2fsprinklerforum.lists.firesprinkler.org&c=E,1,fNY6OnDcAmTS40jZb5yrvgCJJgzbczzQE5iMOvOr9vO9i1_Rv-Z7CcH0vDjL1cZBqahcB_34qWnM7TPsY0N7FSxJJs46NGOahc6MzP8HLERbJPw,&typo=1__;JSUlJSU!!FaxH778!aqlEnecQGHKgLBtlqiH-zwJML521Ca91RuxZ6cKDLhbusSC-2uzEAhs-0m2Dgp9kOr15roxWdK6EhyRS$>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to