Brett, here is Todd’s take (having seen a lot of pumps with issues lately):
  

  
1. Make sure you have the 10X pipe diameter distance between the backflow 
preventer and the pump suction.   
  

  
2. Based on the pump test, you have a 750 gpm pump rated at 70 psi and 
producing only 65 psi at 750 gpm during the test. 63 psi would be a failed 
test. How does that compare with previous tests? It could be an issue with the 
pump or the suction piping. It is a 51 year old pump. Needs investigating.   
  

  
3. You need to get a hydrant flow test. I wouldn’t touch a pump project without 
one.   
  

  
4. You need to do a standpipe calculation to see what your demand is at the 
pump discharge.   
  

  
5. Don’t draw the public supply below 20 psi during a test.
  

  
6. There is a section in NFPA 25 that states that if a pump cannot be tested to 
150%, but it can be tested to the greater of system demand or rated flow, then 
it can be considered acceptable.   
  
  
  
Todd G Williams, PE  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-535-2080 (tel:860-535-2080)  (ofc)
  
860-554-7054 (tel:860-554-7054)     (fax)
  
860-608-4559 (tel:860-608-4559)  (cell)
  
  
  
  

  
  
>   
> On Mar 6, 2026 at 10:52 AM,  <Chris Dorn 
> (mailto:[email protected])>  wrote:
>   
>   
>           
>   
>
>   Questions
>
>   
>   
>   If testing confirms the standpipe cannot achieve 65 psi at 750 GPM, what is 
> the recommended course of action?
> Install a higher pressure fire pump. 150% is not a requirement. 65psi 
> definitely is though. Fire pumps make pressure, not water.   
>  How should we address the requirement for a backflow preventer when pump 
> suction is already low at 150% flow?
>   
>   
>
>   Again not a requirement.
>
>   
>   
>  Are there alternative design approaches to meet the water authority’s 
> requirement while maintaining proper pump operation?
>   
>   
>
>   The water purveyor is protecting their system from a backflow situation. 
> They are not going to let this go.
>
>   
>   
>  Water authority wants the backflow detector assembly on the suction side of 
> the pump.
>   
>   
>
>   Find the lowest pressure loss backflow device and go with it.
>
>   
>
> Just my opinion.
>
>   
>
> Chris
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>   
>   
>
>  From:    Brett Barrall  <[email protected]>
>   Sent:  Friday, March 6, 2026 9:55 AM
>   To:  [email protected]
>   Subject:  [Sprinklerforum] Backflow Preventer on Fire Pump Suction
>
>   
>   
>   
>
>   
>
>   
>
> Hello!
>
>   
>
>   
>
>   
>
> This is my first time posting, I’ll try to keep it short.
>
>   
>
>   
>
>   
>
>   We have a project with a new customer where the water authority is 
> requiring a backflow preventer on the suction side of an existing fire pump. 
> We want to confirm the proper approach due to potential hydraulic concerns.
>
>   
>   
> Building height: 130 ft
>   
> System type:    Wet pipe sprinkler and standpipe  
>   
> Stair Tower 1: Class III combined automatic standpipe
>   
> Stair Tower 2: Automatic Class III standpipe
>   
> Standpipe flow requirements – 65 psi at 750 gpm (System installed 1975)
>   
>   
>   
>   
>
>   
>
>   
>   
> Fire pump: 70 psi at 750 GPM, city main supply
>   
> Hydrant flow test not performed, assuming static pressure at street around 75 
> psi.
>   
> No standpipe flow information. I recommended a standpipe flow test to be 
> performed for documentation purposes.
>   
>   
>
>     
>
>   
>
>    Existing Suction Piping
>
>   
>   
> 4” × 6” concentric reducer at pump suction flange, recommended replacement 
> with 4” × 6” eccentric reducer
>   
> 1975 water meter to be removed during backflow installation. Couldn’t find 
> data sheets on this water meter to determine friction loss at system demand.
>   
>   
>
>     
>
>   
>
>   Pump Test Data
>
>   
>
>   
>
>   
>   
>   
>   
>   
>
>   Flow
>
>   
>   
>   
>
>   Suction Pressure
>
>   
>   
>   
>
>   Discharge Pressure
>
>   
>   
>   
>   
>   
>
>   Churn
>
>   
>   
>   
>
>   75 psi
>
>   
>   
>   
>
>   155 psi
>
>   
>   
>   
>   
>   
>
>   100% (750 GPM)
>
>   
>   
>   
>
>   45 psi
>
>   
>   
>   
>
>   110 psi
>
>   
>   
>   
>   
>   
>
>   150% (1125 GPM)
>
>   
>   
>   
>
>   5 psi
>
>   
>   
>   
>
>   50 psi
>
>   
>   
>   
>   
>   
>
>   
>
>   
>
>   Sprinkler system demand: 268 GPM at 68 psi
>
>   
>   
>   Light Hazard
>   
>   Apartments
>   
>   
>
>     
>
>   
>
>   Concern
>
>   
>   
> At 150% flow, suction is already 5 psi without a backflow preventer.
>   
> Adding a backflow preventer with additional fittings will introduce friction 
> loss and will pull city main below zero during high demand.
>   
>  Preliminary calculations indicate the standpipe may not achieve 65 psi 
> residual at 750 GPM; (System installed 1975), verification pending a 
> standpipe flow test.
>   
>   
>
>     
>
>   
>
>   Questions
>
>   
>   
> If testing confirms the standpipe cannot achieve 65 psi at 750 GPM, what is 
> the recommended course of action?
>   
> How should we address the requirement for a backflow preventer when pump 
> suction is already low at 150% flow?
>   
> Are there alternative design approaches to meet the water authority’s 
> requirement while maintaining proper pump operation?
>   
> Water authority wants the backflow detector assembly on the suction side of 
> the pump.
>   
>   
>
>     
>
>   
>
>     
>
>   
>
>   Thank you for any guidance.
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>
>  Thank You,
>
>   
>
>     
>
>   
>
>  Brett Barrall
>
>   
>
> Fire Sprinkler Designer
>
>   
>
> [email protected] (mailto:[email protected])
>
>   
>
>   
>
>   
>
>           
>
>   
>
>   
>
>   
>
>   50 S. Museum Road, Reading, PA 19607 (https://goo.gl/maps/A3D5Y6oTJUT2)
>
>   
>
> Office: 610-775-1200   ●    Toll Free: 1-800-344-4012
>
>   
>
> www.bsgi.com (https://www.berkshiresgi.com/)
>
>   
>
>  Satellite Offices in York  &  State College
>
>   
>
> ●PA State Contract  &  Costars Participating Vendor   ●
>
>   
>
>   ----- Email Disclaimer -----
>  This email and any files transmitted with it are confidential and are 
> intended for the named recipient(s). If you are not the intended recipient, 
> you are hereby notified that you have received this communication in error 
> and that any copying, disclosure, dissemination, distribution or review of it 
> or its contents is prohibited. If you have received this email in error, 
> please notify the sender and immediately delete this email from your system.
>
>   
>
>   
>
>   
>  _________________________________________________________ SprinklerForum 
> mailing list: 
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> To unsubscribe send an email to [email protected]
>   
  
  
     
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to