Craig,

Is he seriously worried that a pipe joint, buried underground with either a thrust block, or a mechanical thrust restraint device is going to move up to 8" when pressurized?

Flanged joints don't permit that much movement, if any, and the last time I looked closely at NFPA-24 flanged fittings were acceptable.

What on Earth is he going on about?
Ken Wagoner, SET
Parsley Consulting
3002 Younger Drive
Harrisonville, Missouri 64701-3909

Phone: (760) 745-6181
Visit the website



On 3/10/2026 9:13 AM, Prahl, Craig wrote:

Thanks Steve.  This condition is way outside the normal scope of seismic issues we typically deal with inside buildings. 

 

The seismic movement condition the ME is worried about was between the pump building and the underground fire main.  So, traditional seismic assemblies won’t work since this needs to be able to be buried in the dirt. 

 

Craig Prahl | Jacobs | Fire Protection SME – EV, AM, DC, Special Hazards

[email protected] | www.jacobs.com

1041 East Butler Road   Greenville, South Carolina  29606

CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS

 

From: Welsh, Steve <[email protected]>
Sent: Tuesday, March 10, 2026 9:31 AM
To: Mike Watts <[email protected]>; Discussion list on issues relating to automatic fire sprinklers <[email protected]>
Subject: [EXTERNAL] [Sprinklerforum] Re: Flexible assembly on pump discharge in seismic cat D area

 

Craig, Not sure if this was your question too. “An approved seismic separation assembly shall be installed where sprinkler piping, regardless of size, crosses building seismic separation joints at ground level and above.” Normally,

Craig,

 

Not sure if this was your question too. “An approved seismic separation assembly shall be installed where sprinkler piping, regardless of size, crosses building seismic separation joints at ground level and above.” Normally, you do not need a separation at the building foundation slab as the slab moves with the ground. However as you are going through a building exterior wall, the wall could move differently than the ground. Thus, the extra separation is required.

 

Notes: There are clearance requirements at the foundation slab. There will also be clearance requirements at the exterior wall. You will some type of flexible weather seal.

 

Steve Welsh, PE  \  Burns & McDonnell

Senior Fire Protection Engineer

M 410-978-3836 

 

From: Mike Watts <[email protected]>
Sent: Monday, March 9, 2026 5:52 PM
To: Discussion list on issues relating to automatic fire sprinklers <[email protected]>
Subject: [Sprinklerforum] Re: Flexible assembly on pump discharge in seismic cat D area

 

 

Mike Watts  RME-G-3218231

Sprinkler Service Manager

Image removed by sender. image

Firetrol Protection Systems, Inc.

4616 W. Howard Lane, Building 7, Suite 700

Austin, Texas 78728

[email protected]

Office 512-687-0115

Cell 512-660-4411


From: Prahl, Craig <[email protected]>
Sent: Tuesday, February 10, 2026 9:28:47 AM
To: Sprinklerforum <[email protected]>
Subject: [Sprinklerforum] Flexible assembly on pump discharge in seismic cat D area

 

I have a packaged fire pumphouse, discharge exists horizontally through the wall and then turns down to connect to the underground outside of the bldg. The seismic design category SDC) is “D”. I am being told by the project ME that we should

I have a packaged fire pumphouse, discharge exists horizontally through the wall and then turns down to connect to the underground outside of the bldg.

 

The seismic design category SDC) is “D”. 

 

I am being told by the project ME that we should have a flexible connection on the discharge side outside the bldg. to accommodate the potential of 8-inches of movement between the pumphouse and underground piping system.

 

I’ve looked around to try and find such an assembly for 8” pipe suitable for an outdoor installation and so far haven’t found such a device.

 

So, my question for those out there in seismically active areas, is this standard practice and who makes such an assembly? 

 

Craig Prahl | Jacobs | Fire Protection SME – EV, AM, DC, Special Hazards

[email protected] | www.jacobs.com

1041 East Butler Road   Greenville, South Carolina  29606

CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS

 

 



NOTICE - This communication may contain confidential and privileged information that is for the sole use of the intended recipient. Any viewing, copying or distribution of, or reliance on this message by unintended recipients is strictly prohibited. If you have received this message in error, please notify us immediately by replying to the message and deleting it from your computer.




NOTICE - This communication may contain confidential and privileged information that is for the sole use of the intended recipient. Any viewing, copying or distribution of, or reliance on this message by unintended recipients is strictly prohibited. If you have received this message in error, please notify us immediately by replying to the message and deleting it from your computer.

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to