Yes, backflow preventers reduce static pressure and the amount depends on the 
device.  Look at the performs curves of the device.  A typical double check 
will have a 4 PSI reduction in static pressure across the device at 0 GPM .
Sincerely,
Joe Kuerzi Jr.

           Certified Protection Services LLC
                  175 Sky Aire Rd. NW 
                   Corydon, IN 47112

 Fire Protection & Water Back-flow Prevention Systems
   Installation, Maintenance, Repair, & Inspections

Contact - Joseph C. Kuerzi Jr., SET
812-738-2970 office
502-551-8530 mobile *preferred
[email protected] 

    On Thursday, August 13, 2026 at 09:07:35 AM EDT, Matt Grise 
<[email protected]> wrote:  
 
  
  
 
do backflow preventers typically reduce static pressure? The charts provided 
with BFP's do show a loss at 0gpm, but is loss the same when flow is increasing 
and decreasing? I usually apply the pressure loss from a BFP at a flowing 
condition, so I'm not sure how they affect static condition.
 
  
 
Anyone know?
 
  
 
Thanks!
 
  
 
Matt Grise
 