Minimum requirement on a standard DCVA is 1 psi drop across each check,
factory curve is usually higher but at less than 1 you have to replace the
check valve, unless you are using a FP DCVA, they are allowed to go to 0.5
psi but I rarely see anyone using them

Thank You
Brett Peters
PFPS Ltd
(780) 777 0568
Sent From My iPhone


On Thu, Aug 13, 2026 at 8:09 AM Travis Mack <[email protected]> wrote:

> I think the question revolves around setting of PRVs.  If you have a
> reduction of 4 psi static from a backflow device, that is ±9' and may be
> enough to save you a PRV.  I have always erred on the side of caution and
> not taken the reduction in static at zero flow.  But I am eager to hear
> from the industry how this is out in the field.
>
>
>
> Travis Mack, SET
>
> *MEPCAD* | Instructor / Training
>
> 181 N. Arroyo Grande Blvd. #105
> <https://www.google.com/maps/search/181+N.+Arroyo+Grande+Blvd.+%23105?entry=gmail&source=g>
> I Henderson, NV 89074
>
> *www.mepcad.com* <http://www.mepcad.com/> | 303-923-8215
>
> *Email: [email protected] <[email protected]>*
>
>
>
> *AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD*
>
>
>
> *Academy of Fire Sprinkler Technology *| Executive Director
>
> 101 S Main Street, Suite 001, Decatur, IL 62523
> <https://www.google.com/maps/search/101+S+Main+Street,+Suite+001,+Decatur,+IL+62523?entry=gmail&source=g>
>
> ------------------------------
> *From:* Henry Leon <[email protected]>
> *Sent:* Thursday, August 13, 2026 8:57 AM
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> [email protected]>
> *Subject:* [Sprinklerforum] Re: static pressure loss through backflow
>
> You don't often get email from [email protected]. Learn why this
> is important <https://aka.ms/LearnAboutSenderIdentification>
>
> Hi Matt,
>
> Yes they typically impact the static pressure which means there is an
> impact at very low flows which becomes important in 13R applications.
>
>
>
> Henry Leon
>
>
>
> *From:* Matt Grise <[email protected]>
> *Sent:* Thursday, August 13, 2026 9:06 AM
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> [email protected]>
> *Subject:* [Sprinklerforum] static pressure loss through backflow
>
>
>
>
>
> do backflow preventers typically reduce static pressure? The charts
> provided with BFP's do show a loss at 0gpm, but is loss the same when flow
> is increasing and decreasing? I usually apply the pressure loss from a BFP
> at a flowing condition, so I'm not sure how they affect static condition.
>
>
>
> Anyone know?
>
>
>
> Thanks!
>
>
>
> Matt Grise
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to