Remember , a floor drain is only acceptable IF it can handle the full flow of a main drain test including an operational fire pump if installed. Normally I size the floor drain to handle the flow for at least 60 seconds.

Having an adequate drain is a requirement of every sprinkler system designed and installed for in accordance with NFPA 13.

Thanks,

John


John August Denhardt, P.E

Vice President Engineering and Technical Services
American Fire Sprinkler Association
301-343-1457

Are you a member with a technical question? 

Don't forget one of the most valuable resources that AFSA provides is Technical Reviews by our Technical Services Department. It’s like having an FPE on your staff. Visit www.firesprinkler.org/technicalreview to submit a question today! (Member login required.)  


On Aug 25, 2026, at 08:46, daren welborn <[email protected]> wrote:



Never heard of that, I cant count how many times I sent a drain to floor drain.

 

From: Tim Easter <[email protected]>
Sent: Monday, August 17, 2026 8:07 AM
To: Discussion list on issues relating to automatic fire sprinklers <[email protected]>; [email protected]
Subject: [Sprinklerforum] Help

 

What code section, mandates that main drain only have one valve if flows outside. 