| Remember , a floor drain is only acceptable IF it can handle the full flow of a main drain test including an operational fire pump if installed. Normally I size the floor drain to handle the flow for at least 60 seconds. Having an adequate drain is a requirement of every sprinkler system designed and installed for in accordance with NFPA 13. Thanks, John John August Denhardt, P.E Vice President Engineering and Technical Services American Fire Sprinkler Association 301-343-1457 Are you a member with a technical question? Don't forget one of the most valuable resources that AFSA provides is Technical Reviews by our Technical Services Department. It’s like having an FPE on your staff. Visit www.firesprinkler.org/
Never heard of that, I cant count how many times I sent a drain to floor drain. From: Tim Easter <[email protected]>
What code section, mandates that main drain only have one valve if flows outside. _________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected] |