I don’t know about calculations or velocities or capacities, but I do know that 
about 98% of our work is in California where there are storm drain pollution 
prevention regulations in just about every county now.  The prevailing 
regulatory standard is that sprinkler test and drain discharges shall not 
terminate in such a way that water can run across hardscape and hit the storm 
drain system.  That means it goes to softscape where it can percolate into the 
ground, or to the sanitary sewer system.   We’ve been detailing a 4” trap with 
a 4” x 6” hub AFF and we’ve never been notified that there is a problem with 
backup during use of any of them (hundreds and hundreds of applications), 
whether it’s for testing, draining or a full-flow MD test.    So I guess that 
sizing works pretty well, though I can’t substantiate why, hydraulically.   

 

CA is not the only state that’s regulating sprinkler discharge, but to my 
knowledge there are no published standards of care for resolving sprinkler 
discharge specifically. 

 

 

Steve L. 

 

From: Casey Milhorn <[email protected] <mailto:[email protected]> > 
Sent: Tuesday, August 25, 2026 6:26 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected] 
<mailto:[email protected]> >
Subject: [Sprinklerforum] Re: Help

 

Great point, and if you have ever done those calculations properly, you will 
find that your drain size is WAY more than the mechanical engineer and general 
contractor typically wants to put in, and it affects the drain pipe size 
downstream significantly sometimes. The cost for upsizing the floor drain may 
far outweigh the cost of routing your main drain to an exterior wall.

 

Casey Milhorn

 

From: John Denhardt <[email protected] 
<mailto:[email protected]> > 
Sent: Tuesday, August 25, 2026 8:14 AM
To: [email protected] 
<mailto:[email protected]> 
Subject: [Sprinklerforum] Re: Help

 

        
You don't often get email from [email protected] 
<mailto:[email protected]> . Learn why this is important 
<https://url.avanan.click/v2/r01/___https:/aka.ms/LearnAboutSenderIdentification___.YXAzOnByb3RlY3Rpb25kZXNpZ25hbmRjb25zdWx0aW5nOmE6bzo0ZjAwOGQ1M2I5NGE2ZmQwZTE4MWM0ZWVjZjM1ODBlOTo3OjIyZTc6YzM1NDRlYzNkN2ZlODMwOGU4MWQ3NDE4ZjFhNzZjNDE2ZDcyYmUzZGEzZGNlMDkwOWNmMTZhNWFmMWZjY2RiZDpoOlQ6Rg>
  

        

Remember , a floor drain is only acceptable IF it can handle the full flow of a 
main drain test including an operational fire pump if installed. Normally I 
size the floor drain to handle the flow for at least 60 seconds. 

 

Having an adequate drain is a requirement of every sprinkler system designed 
and installed for in accordance with NFPA 13. 

 

Thanks,

John

 

John August Denhardt, P.E

Vice President Engineering and Technical Services

American Fire Sprinkler Association

301-343-1457

 

Are you a member with a technical question? 

Don't forget one of the most valuable resources that AFSA provides is Technical 
Reviews by our Technical Services Department. It’s like having an FPE on your 
staff. Visit www.firesprinkler.org/technicalreview 
<https://url.avanan.click/v2/r01/___https:/www.firesprinkler.org/technicalreview___.YXAzOnByb3RlY3Rpb25kZXNpZ25hbmRjb25zdWx0aW5nOmE6bzo0ZjAwOGQ1M2I5NGE2ZmQwZTE4MWM0ZWVjZjM1ODBlOTo3OmIwZjQ6ZmNhMjg3NmIyNmY5N2U3OGNkNTFiMTM4ZjNhOTk4NTJmN2VjMzcwZDg0NTliOWEwOGIwNWYwMmQ2YTIzYTAzYzpoOlQ6Rg>
  to submit a question today! (Member login required.)  


On Aug 25, 2026, at 08:46, daren welborn <[email protected] 
<mailto:[email protected]> > wrote:

 

Never heard of that, I cant count how many times I sent a drain to floor drain.

 

From: Tim Easter <[email protected] <mailto:[email protected]> > 
Sent: Monday, August 17, 2026 8:07 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected] 
<mailto:[email protected]> >; 
[email protected] 
<mailto:[email protected]> 
Subject: [Sprinklerforum] Help

 

What code section, mandates that main drain only have one valve if flows 
outside. 


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
<https://url.avanan.click/v2/r01/___https:/lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org___.YXAzOnByb3RlY3Rpb25kZXNpZ25hbmRjb25zdWx0aW5nOmE6bzo0ZjAwOGQ1M2I5NGE2ZmQwZTE4MWM0ZWVjZjM1ODBlOTo3OjhkMTI6MmQ1NDQ0MmMxMThlODcxNGUxM2EzMGQwODM1OWU5ZjBlYzY3ODRkYmVjNTcyYzkxZDdiYzUxOTVmMzA2OTY5NTpoOlQ6Rg>
 
To unsubscribe send an email to [email protected] 
<mailto:[email protected]> 

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to