American Fire Sprinkler Association
9696 Skillman., #300 Dallas, Texas 75243
Ph:  (214) 349-5965       Fax:  (214) 343-8898


-----------------------------------------
TECHNICAL UPDATE
November 8, 2006
---------------------------------

"We request a determination on non-combustible buildings above the ceilings whether if sprinklers are required per IBC 903.3.1.1.1. Number 4. The fire department does not allow smoke detectors above the ceilings, only sprinklers because of electrical lines that are not in conduit, and for computation on plastic on round air ducts. If the space is not 100 percent wholly non-combustible, sprinklers are required. It looks to me that all non-combustible buildings will never be wholly non-combustible and under IBC without smoke detection, sprinklers will always be required. Do you see this happening across the country?"

We have reviewed the 2002 Edition of NFPA 13 and the 2006 International Building Codes as the applicable standard and code. Our informal interpretation is that some minor quantities of combustible materials, such as communication wiring, can be present in some concealed spaces but should not be viewed as requiring sprinklers or automatic fire detection system.

Referencing IBC 903.3.1.1 states sprinklers shall be installed throughout in accordance with NFPA 13 except as provided in section 903.3.1.1.1. This section is exempting additional rooms or areas if an automatic detection system is installed. The exempt locations listed in the IBC would normally require sprinklers according to NFPA 13. In other words, the IBC is exempting additional locations from sprinklers required by NFPA 13 if an automatic fire detection system is installed. In addition, the intent of 903.3.1.1.1 is not to add automatic detection devices to rooms or areas exempt from sprinklers by NFPA 13.

The NFPA 13 handbook explanatory text clarifies above ceiling spaces in section 8.14.1.1. This states some minor quantities of combustible materials, such as communication wiring, can be present in some concealed spaces but should not be viewed as requiring sprinklers. If bundles of unsheathed computer wiring are installed above the ceiling or beneath the floor in as manner where fire propagation in all directions is likely, then the concealed space should be treated the same as a combustible space, thereby requiring appropriate sprinkler protection. This example was based a computer facility were you have a concentrated use of infrastructure type materials as opposed to the typical minor amount found in every building. In conclusion, this concealed space should not require sprinklers or automatic fire detection system.

------------------
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees.

Copyright (c) 2006, American Fire Sprinkler Association. All Rights Reserved
--------------------------