Documentation was provided on a pump that will be used as part of a temporary water supply. The pump was not listed, but it was under a 500 gpm rated capacity. The municipal water supply is not readily available and will be provided in the future with no date specified. A pond is being designed that will have a primary function of supporting the water storage requirements for fire suppression. A fire pump will be required to support the fire sprinkler system for a 50,000 sq. ft. athletic complex. The engineer recommended a submersible pump in the pond as the most appropriate and cost- effective option for the temporary fix. You asked the following question,

"IS A NON-LISTED FIRE PUMP ACCEPTABLE FOR THIS APPLICATION?"

We have reviewed the 2003 edition of NFPA 20 as the applicable standard. Our informal interpretation is that other types of pumps can be used, but still have to be listed by a testing laboratory and meet the applicable requirements of NFPA 20.
a
NFPA 20 indicates in section 5.7.1 "fire pumps shall be dedicated to and listed for fire protection service." The annex material does not preclude the use of pumps in public and private water supplies that provide water for domestic, process, and fire protection purposes. However, this application is a pump strictly dedicated as a water supply to a sprinkler system and shall be listed. Referring back to section 5.1.2 states, "other than those specified in this standard and having difference design features shall be permitted to be installed where such pumps are listed by a testing laboratory." The NFPA 20 standard currently recognizes horizontal and vertical split case, in-line, and vertical shaft type pumps. The intent of this section is that other types of pumps can be used such as "submersible," but still must be listed by a testing laboratory to show that it will provide the flows necessary for the application. The limitation on the 500 gpm capacity covers a safety factor for pumps not addressed by NFPA 20 by only permitting these pumps on small systems. It is not the intent of this section that when a demand is below 500 gpm, an off the shelf non-UL Listed pump can be used, placed in a pond, and not follow any other NFPA 20 requirements. This application still has to meet wet pit, trash rack, leaf screen, and strainer requirements. Additional requirements including the piping arrangements, underground piping, aboveground pipe and fittings, power supplies, controllers, protection from freezing, and testing requirements have to be addressed. The documentation does not specify how the pond will be replenished to maintain the water level. In closing, other types of pumps can be used such as submersible types provided the pump is listed and the installation conforms to all applicable NFPA 20 requirements.
------------------
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees.

Copyright (c) 2006, American Fire Sprinkler Association. All Rights Reserved
--------------------------
If you'd rather not receive future faxes from AFSA, fax your removal request to (888) 839-4830 or e-mail @ [EMAIL PROTECTED] Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful.



_______________________________________________
Sprinklernotes mailing list
[EMAIL PROTECTED]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to