NFPA 13 - USING BAFFLES
As directed by 13:8.5.3.4, we are required to maintain a minimum distance between sprinklers in order to avoid an operating sprinkler from wetting an adjacent sprinkler (cold-soldering) and causing skipping within the remote area. So lets say you have an ESFR system and due to a structural or mechanical issue you have two sprinklers that are only 6 ft apart. What do you do? Most immediately say install a baffle and keep on going. This presents a problem. The use of baffles to account for less than the minimum separation is addressed in 13:8.6.3.4.2 and 8.8.3.4.2. These two sections cover standard pendent and upright sprinklers and extended coverage pendent and upright sprinklers. Thus, baffles can be used be used ONLY for these types of sprinklers. The moral of the story is that LOCATION HAS MEANING.

DRY PENDENT SPRINKLERS AND DROP NIPPLES
The question has arisen on whether dry pendent sprinklers can be installed on a sprinkler drop nipple. In a dry pipe system, this is an easy no since water would collect in the drop nipple and be subject to freezing. Even in an area that is not subject to freezing there is concern about scale and sediment settling on the top of the dry type sprinkler. This is pointed out for dry pipe systems in A. 7.2.2 (2). The allowance in 7.2.2(3) for return bends does not apply either since the sprinkler must also be in the heated area. In a wet system, such as where one is dropping down to protect a small cooler or freezer, it gets a little ambiguous. There is nothing in NFPA 13 on it except the general requirement to apply the listing requirements. This takes us to the manufacturer's installation sheets. These sheets limit dry pendent sprinkler to be installed only in a tee. One even states not to be connected to a coupling in a drop nipple. This does not mean you can't use it. It just means you install it in the through side of the tee. Despite 8.15.2.5.3.2 saying auxiliary drains are not for drops supplying dry pendent sprinklers, dealing with the water for a sprinkler penetrating a freezer could be messy. As such, a tee provides a drain for the drop and meets the protrusion into the fitting requirement (i.e. a tee). Obviously, the minimum required barrel length to avoid freezing is measured to the point of connection.


MARK YOUR CALENDARS FOR CENTER FOR LIFE SAFETY EDUCATION AND AFSA UPCOMING SEMINARS VIRTUAL SEMINAR

10 COMMON DESIGN MISTAKES & HOW TO AVOID THEM
February 28, 2007
12:00 PM Eastern
11:00 AM Central
10:00 AM Mountain
9:00 AM Pacific

Earn:  0.15 CEU's  / 1.5 CPD's.

Event ID: 12438

To Register:
By Phone: 800-775-7654, please have your credit card information ready.
By Fax: 800-676-0734  Fax completed form with Credit Card information.
Online: www.krm.com/clse


2007 AFSA DESIGN SCHOOLS

Beginning System Planning School

January 29-February 9, 2007 Sold Out!
February 19-March 2, 2007 Sold Out!
April 30-May 11, 2007 Sold Out!
June 18-29, 2007
August 6-17, 2007
October 8-19, 2007
November 5-16, 2007
December 3-14, 2007

Registration Prices:
Member  $1200
Non-Member   $1700

2007 Intermediate Design School

March 26-30, 2007 Enroll Early
Registration Prices:
Member  $ 800
Non-Member   $ 1000

SEMINARS/CONVENTIONS

OSU Fire Sprinkler Inspection Training & Certificate Program
February 8-10,2007
March 26-28,2007
April 30-May 2,2007
Stillwater, Oklahoma

----------------------------------------------
TechTalk is prepared by the Technical Services Department of the American Fire Sprinkler Association: Vice President of Engineering and Technical Services, Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a CFPS and a NICET IV certified automatic sprinkler technician, and Tom Wellen, a degreed fire protection-engineering technologist. Opinions are provided with the understanding that AFSA assumes no liability for the opinions or actions taken on them and they are not to be considered the official interpretation of the NFPA or that of its technical committees.

Copyright (c) 2007, American Fire Sprinkler Association, 9696 Skillman St., Suite 300, Dallas, TX 75243. Voice (214) 349-5965 ext 124 or Fax (214) 343-8898. All rights reserved.
------------------------------------------------

_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to