American Fire Sprinkler Association
12750 Merit Drive, Suite 350   Dallas, TX 75251
Ph:  (214) 349-5965       Fax:  (214) 343-8898


TECHNICAL UPDATE
FEBRUARY 8, 2007

------------------------------------------------------------------------ ------ AFSA moving February 15-16, 2007. Please make a note of our new address effective February 19th. Our phone and fax numbers will NOT change. Informal interpretation requests during this time will e answered as time permits; do to the move. Thank you.

12750 Merit Drive, Suite 350
Dallas, TX 75251
------------------------------------------------------------------------ -------

"We have a small peaked warehouse protected with a dry system. The cross main on one side of the peak drains to the riser. The cross main on the other side is trapped and has a drum drip at the end of the main. There is no heat in the building and the drum drip must be installed for the trapped main. Is it against the requirements of NFPA 13 to have a drum drip in a freezing area?"

We have reviewed the 2002 Edition of NFPA 13 that you have identified as the applicable Standard. Our informal interpretation is that it is acceptable to locate a drum drip in an area that is subject to freezing.

It is preferable to locate drum drips or auxiliary drains on dry systems in a heated area. This is not always possible to accomplish this in a dry pipe sprinkler system. NFPA 13:8.15.2.5.3 discusses the size and type of drains for dry pipe systems in areas subject to freezing. The 2002 Edition of NFPA 13 is not as clear as the 2007 Edition on the issue of these drains being located in an area that is subject to freezing. The 2007 Edition in Subsection 8.16.2.5.3.1 helps to clear this issue up by stating: "Auxiliary drains located in areas subject to freezing shall be readily accessible."

Therefore, NFPA 13 does allow drum drip drains on dry pipe systems to be located in areas subject to freezing. This will put an additional responsibility on the user of the system to keep the drum drips properly drained during the freezing seasons. The owner/user of the dry pipe system needs to be informed of the location of all low point drains in the system. The 2002 Edition of NFPA 25 "Standard for the Inspection, Testing, and Maintenance of Water-Based Fire Protection Systems" also address requirements for low point drains in dry systems in Table 5.1 and in Subsection 12.4.4.3.3.


-----------------
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees.

Copyright (c) 2007, American Fire Sprinkler Association. All Rights Reserved
--------------------------