"I have a soffit that is over 30 inches wide. When referencing NFPA 13:8.6.5.1.2, I can locate my sprinkler head accordingly to comply with (#1) subsection 8.5.5.2, table 8.6.5.1.2 and figure 8.6.5.1.2 (a). However I do not comply with (#3) obstructions located against the wall and that are not over 30 inches in width shall be permitted to be protected in accordance with figure 8.6.5.1 (b). Are sprinkler heads required under the soffits over 30 inches wide to provide adequate coverage below the soffits?"

We have reviewed the 2002 Edition NFPA 13 as the applicable Standard. Our informal interpretation is that sprinklers will not be required under soffitts that are over 30 inches in width if you comply with the "Beam Rule" requirements of Figure 8.6.5.1.2 (a) and Table 8.6.5.1.2.

Confusion can exist between applying the requirements of obstruction against walls (Soffit Rule) and the obstructions to sprinkler discharge (Beam Rule). The Soffit Rule: Figure 8.6.5.1.2 (b) applies to soffits up to and including 30-inches in width and can not be used for soffits that are wider then that. A note on soffits that must be addressed is that to qualify as a soffit; it must have a solid bottom plate. You cannot apply the soffit application to a Valance, which will not be enclosed at the bottom plane. The advantage that the Soffit Rule over the Beam Rule is shown in Figure 1 is that the Soffit Rule allows you to locate a sprinkler closer to the wall then what would be allowed by the use of the Beam Rule. This is one of the reasons why the Soffit Rule is not allowed to be applied to soffits that exceed 30-inches in width.

As shown in Figure 1, we have a soffit that is 18-inches deep and 30- inches wide. The deflector of the sprinkler in both the Soffit Rule and Beam Rule applications is located 3-inches down from the ceiling.


The Soffit Rule (A≥ (D - 8 in.) + B) will allow the sprinkler to be located 3 ft. 1 inch (30 - 8 + 15 (18 - 3) = 37 inches) from the side of the soffit. Appling the Beam Rule to this same situation, with the sprinkler deflector located 15-inches above the bottom of the soffit, the closest that the sprinkler can be located to the side of the soffit using Table 8.6.5.1.2 is 4-ft. 6-inches.

So as shown, the Soffit Rule will allow a sprinkler to be located closer to the soffit then the Beam Rule. If the sprinkler cannot meet either application, an additional sprinkler will have to be installed beneath the soffit. When applying either rule, the area of coverage of the sprinkler is determined by the distance of the sprinkler from the wall and not from the side of the soffit.
-----------------
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees.

Copyright (c) 2007, American Fire Sprinkler Association. All Rights Reserved
--------------------------
If you'd rather not receive future faxes from AFSA, fax your removal request to (888) 839-4830 or e-mail @ [EMAIL PROTECTED] Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful.

 _______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to