A sprinkler pipe is located in a corridor that supplies both sprinklers in the corridor and branch lines to the living units. The pipe is concealed above drywall ceilings except for the stair in a nine-story building. You have asked the following question:

"Are flushing connections required at end of 11/2-in. diameter CPVC sprinkler lines with sprinkler drops directly attached to 11/2-in. lines?"

We have reviewed the 2002 Edition of NFPA 13 you indicated as the applicable Standard. Our informal interpretation is that flushing connections are required.

CPVC pipe is not exempt from flushing connections. The CPVC pipe does not have corrosion issues with the piping, but there is a potential of foreign materials entering the system. Section 8.14.16 is clear that all sprinkler systems shall be arranged for flushing, readily removable fittings shall be provided at the end of all cross mains, and all cross mains shall terminate in 11/4-inch or larger pipe. The piping in the corridor is serving two purposes. One, it supplies the sprinklers in the corridor, and the other is to supply branch lines to the residential living units. The confusion lies within the piping in the corridor meeting both definitions of a branch line and a cross main. The corridor piping fits closer to the definition of a cross main, thus flushing connections would be required.

-----------------
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees.

Copyright (c) 2007, American Fire Sprinkler Association. All Rights Reserved
--------------------------