"Are residential sprinklers allowed above ceiling fan blades? The local AHJ indicated to follow the 2007 edition of NFPA 13R. We have not obtained a copy of this document yet and the installation is complete."

We have reviewed NFPA 13R, 2002 edition, which you indicated as the applicable standard. Our informal interpretation is that sprinklers can be located above fan blades. However, the sprinklers must be placed to meet the obstruction rules.

NFPA 13R section 6.7.1.5.3 states, "Sprinklers shall be positioned so that the response time and discharge are not unduly affected by obstructions such as ceiling slope, beams, or light fixtures. But, there are no explicit criteria for how to space the sprinklers from obstructions. Fortunately, the handbook text gives guidance indicating that ceiling fan blades have no adverse effect rotating in either direction. It states that the motor housing is the primary element that can impede the spray pattern and that the vertical obstruction rules from NFPA 13 can be used to minimize the motor's impact as an obstruction. The applicable vertical obstruction rules referenced by the handbook are given in NFPA 13, section 8.10.6.2.1.3 and its Figure. Applying these, you would take the largest dimension of the fan motor housing (probably the diameter) and multiply by four. Ensure that the horizontal separation between the sprinkler and the fan motor housing is this distance minimum, but it does not need to exceed 36 inches. If the ceiling fan motor housing is 6 inches in diameter, then the sprinkler must be at least 24 inches away from the housing. If it is 10 inches in diameter, then the sprinkler needs to only be 36 inches away to satisfy the rule.

The 2007 edition does provide specific guidance for pendent sprinklers. Section 6.8.1.5.3.2 states, "(A) Pendent sprinklers shall be located at least 3 ft from obstructions such as ceiling fans and light fixtures unless the requirements of 6.8.1.5.3.4 are met." and "(B) The distance shall be measured from the center of the sprinkler to the center of the obstruction." This new wording provides clear guidance but is not yet in effect for your application. Thus if you meet the 2002 edition application for obstructions, you met the intent of the standard.
-----------------
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees.

Copyright (c) 2007, American Fire Sprinkler Association. All Rights Reserved
--------------------------
If you'd rather not receive future faxes from AFSA, fax your removal request to Linda Dawson at Efax (214) 242-3155 or call toll free (888) 839-4830 or send e-mail request @ [EMAIL PROTECTED] Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful. _______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to