American Fire Sprinkler Association
12750 Merit Dr., Suite 350 Dallas TX 75251
Ph:  (214) 349-5965       Fax:  (214) 276-0908


TECHNICAL UPDATE
APRIL 11 2007

A diagram was attached showing an elevation view of a glass wall separating a floor level from an atrium. The sprinklers are placed above the glass wall and a horizontal mullion is located 3 ft above the floor. You asked the following question:

"There is an atrium separated from the other areas with a glass wall. Sprinklers are spaced around the glass wall as required by IBC and NFPA. However, there is an intermediate horizontal mullion 3 ft above the floor that does not allow water to completely cover the glass wall. What should be done in order to comply with the code?"

We have reviewed the IBC, 2000 edition and NFPA 13, 2002 edition that you indicated as the applicable code and standard. Our informal interpretation is that the sprinkler must spray on the entire surface of the window and the intermediate horizontal mullion may create an obstruction that may prevent water spray on the entire surface.

The best option for complying with the codes is to communicate the sprinkler requirements to the architect where a pane of glass is provided from floor to ceiling since horizontal mullions present a problem. A handrail several inches from the glass surface could be installed in lieu of the intermediate horizontal mullion if there is any fear of occupants falling through the glass. Another option is to discuss the situation with the authority having jurisdiction on the intermediate horizontal mullion. Perhaps it could be demonstrated that sprinkler coverage is provided to the entire window surface even with the intermediate horizontal mullion.

The IBC and NFPA 13 Annex have the same message of applying water on the entire surface of the glass. Section 404.5 in the IBC states, "A glass wall forming a smoke partition where automatic sprinklers are spaced 6 feet or less along both sides of the separation wall, or on the room side only if there is not a walkway on the atrium side, and between 4 inches and 12 inches away from the glass and designed so that the entire surface of the glass is wet upon activation of the sprinkler system." The later editions of the IBC includes the words "without obstruction" at the end of this section. The information in Annex D.3 also states, "Glass walls and inoperable windows shall be permitted in lieu of the fire barriers where automatic sprinklers are spaced 6 ft apart or less along both sides of the glass wall and inoperable windows, not more than 1 ft from the glass, and with the automatic sprinklers located so that the entire surface of the glass is wet upon operation of the sprinklers." On a side note, the 2007 edition of NFPA 13 now includes information from the Life Safety Code on atriums in section 21.20.1.2.1 that also includes the very similar wording. The information in Annex D.3 was also retained in the 2007 edition.

A listed window sprinkler is available from Tyco Fire & Building Products that is identified as Model WS. This head is a specific application window sprinkler and has orientations for horizontal and pendent vertical sidewall installations. This particular sprinkler was not tested with intermediate horizontal mullions. The window sprinkler data sheet specifically indicates that window sprinklers are not listed to protect windows when intermediate horizontal mullions are present. Thus the intent of the sprinkler manufacturer, IBC, and NFPA 13 is to provide coverage to glass walls in atrium without horizontal obstructions.
-----------------
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees.

Copyright (c) 2007, American Fire Sprinkler Association. All Rights Reserved
--------------------------
If you'd rather not receive future faxes from AFSA, fax your removal request to Linda Dawson at Efax (214) 242-3155 or call toll free (888) 839-4830 or send e-mail request @ [EMAIL PROTECTED] Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful.