Hose Allowance for Limited Area Systems
The question arises concerning hose allowances and are they required for Limited Area Systems? Section 4.2.1 for Limited Area Systems states, "When partial sprinkler systems are installed, the requirements of this standard shall be used insofar as they are applicable." So, even though this design is six sprinklers supplied by the domestic water supply, the requirements of NFPA 13 still apply. The heads are required to be calculated through the domestic water supply. The outside hose stream would be added to the system at the city connection or a yard hydrant, whichever is closer as indicated by section 22.9. The outside hose allowance is to be used for firefighting purposes. However, buildings without fire sprinkler protection will generally have much greater water demands for the needed fire flows fire firefighting than the outside hose allowances indicated in NFPA 13. So why bother with the outside hose allowance? The most important point of Limited Area Systems is section 4.2.2 that states, "The authority having jurisdiction shall be consulted in each case." The AHJ will specify whether the outside hose requirement will be required.

Detection Wire Attached to the Pipe
The support of non-system components is not allowed on sprinkler pipe and hangers. But what about line heat detectors for preaction or deluge systems? Section 9.1.1.7 commentary from the 2007 NFPA 13 Handbook indicates that detectors and wiring associated with a preaction or deluge systems are permitted to be supported by the pipe and hangers because they are system components. However, detection systems not associated with the sprinkler system cannot be attached to the pipe. The Protectowire website, as an example, also posted the following frequently asked question, "Can Protectowire Linear Heat Detector be attached to sprinkler pipes? Answer: Mounting Protectowire Linear Heat Detector directly to sprinkler pipes is common practice when the detector is the initiating component of an extinguishing system. In this instance Protectowire Linear Heat Detector is considered an integral component of the extinguishing system and typically is allowed by most Authorities Having Jurisdiction (AHJ). Consult the local Authority Having Jurisdiction for acceptability prior to installation." When the wires are attached to the pipe, the manufacturers of the line heat detectors supply or have approved mounting hardware and accessories. The use of non- approved mounting hardware and accessories may physically damage the detector thereby causing "false alarms" and in some cases void the detector's warranty.

====================
Mark your calendars for the next Virtual Seminar

NICET TESTING PREPARATION - STUDY MATERIALS FOR INSPECTION & TESTING
May 30, 2007

12:00 PM Eastern
 11:00 AM Central
 10:00 AM Mountain
  9:00 AM Pacific
Earn:  0.15 CEU's  / 1.5 CPD's.
To Register:
Event ID: 12513
         Member:       $70 per connection
     Non Member:        $100 per connection
CEU Certificate:      $40 per listener to receive CEU Certificate

By Phone: 800-676-0734, please have your credit card information ready.
By Fax: 800-775-0754 Fax completed form with Credit Card information.
By Mail: KRM Information Services Inc. PO Box 1187 Eau Claire, WI 54702-1187 (Payment must accompany registration)
Online: www.krm.com/afsa

HOW MUCH IS MY COMPANY WORTH?
June 20, 2007

Seminar and registration details coming soon.


2007 AFSA DESIGN SCHOOLS
Beginning System Planning School
August 6-17, 2007
October 8-19, 2007
November 5-16, 2007
December 3-14, 2007
Registration Prices:
          Member $1200
      Non-Member $1700

SEMINARS/CONVENTIONS
OSU Fire Sprinkler Inspection Training & Certificate Program
April 30-May 2,2007
Stillwater, Oklahoma
NFPA World Safety Convention and Exhibition
June 3-7, 2007
Boston, MA

==========================
TechTalk is prepared by the Technical Services Department of the American Fire Sprinkler Association: Vice President of Engineering and Technical Services, Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a CFPS and a NICET IV certified automatic sprinkler technician, and Tom Wellen, a degreed fire protection-engineering technologist. Opinions are provided with the understanding that AFSA assumes no liability for the opinions or actions taken on them and they are not to be considered the official interpretation of the NFPA or that of its technical committees.

Copyright (c) 2007, American Fire Sprinkler Association, 9696 Skillman St., Suite 300, Dallas, TX 75243. Voice (214) 349-5965 ext 124 or Fax (214) 343-8898. All rights reserved.

If you'd rather not receive future faxes from AFSA, fax your removal request to (888) 839-4830 or e-mail to [EMAIL PROTECTED] Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful.

_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to