American Fire Sprinkler Association
12750 Merit Dr., Suite 350 Dallas TX 75251
Ph:  (214) 349-5965       Fax:  (214) 276-0908

------------------------------
TECHNICAL UPDATE
June 14, 2007
------------------------------

"An existing facility has a new 2,000 sf addition which will contain a mezzanine. There is no separation from the existing facility. It is extra hazard occupancy with a dry pipe system so the size of the remote area should be 3,250 sf. Should I include the mezzanine in defining the size of the new remote area?"

We have reviewed NFPA 13, 2002 Edition, which you indicated, is the applicable standard. Our informal interpretation is that you would not include the mezzanine.

There is no explicit guidance on this issue but other mezzanine criteria shows us the intent. Let's start with 13:8.2.2 that states the floor area of the mezzanine shall not be included in the area limits for the system. The basic philosophy is that a fire under the mezzanine will activate sprinklers below it and not at the higher ceiling. In essence, both are effectively assigned to the same portion of the floor plan. Another supporting issue appears in 13:12.2.2.4, which addresses bin, box with walkways. This is similar to a mezzanine with open grate flooring. Here we are told to have sprinklers under the walkways and the critical part is that we don't add that water demand to the ceiling. In ssence, the mezzanine is treated as a separate area from the ceiling.

The unanswered question is what do you do about the size of the remote area? Unless it is contained by rated construction, you still have to meet the required 3,250 sf. As such, you must include a portion of the existing system within your remote area.

---------------------
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees.

Copyright (c) 2007, American Fire Sprinkler Association. All Rights Reserved
--------------------
If you'd rather not receive future faxes from AFSA, fax your removal request to Linda Dawson at Efax (214) 242-3155 or call toll free (888) 839-4830 or send e-mail request @ [EMAIL PROTECTED] Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful. _______________________________________________