American Fire Sprinkler Association
12750 Merit Drive, Suite 350 * Dallas TX 75251
Ph:  (214) 349-5965       Fax:  (214) 276-0908

------------------------------------
TECHNICAL UPDATE
June 6, 2007
------------------------------------


"A light hazard building had a ceiling height of 12 ft - 4 in. above finished floor was supplied with sprinklers designed at 0.1/1,500 sf with heads spaced at 125 sf max. flowing 12 heads. A tenant moved in adding multiple light hazard offices with ceilings approximately 10 ft above finished floor. Can we use the small room application knowing we will have heads spaced at least 7 ft - 6 in. off three walls and 9 ft off one wall?

We have reviewed NFPA 13, 2002 edition, as the applicable standard. Our informal interpretation is that your proposed arrangement is not acceptable since the maximum area of coverage per sprinkler is exceeded and it appears you are exceeding 7'6" from more than one wall.

The small room design as dictated by 13:8.6.3.2.4 explicitly allows us to exceed the maximum spacing allowance of 7'6" to one wall but the area of coverage and the allowed spacing to the other walls and sprinklers shall not be exceeded. So you can space up to 7'6" to the other walls, whereas you said spaced "at least" 7'6". In calculating the area of coverage, you simply take the area of the room and divide it by the number of sprinklers. The SxL rules do not apply but the maximum spacing dimensions must still be applied If the area of the room calculates to 247 sf, that exceeds the 225 sf maximum area of coverage for a single sprinkler. Two sprinklers would be needed for the room unless a quick response extended coverage sprinkler is used (for which the small room rule does not apply). As an example, Figure A.8.6.3.2.4 (b) shows two sprinklers each 9 ft - 0 in. off one wall and 6 ft - 0 in. off the opposite, 15 ft between sprinklers, and 7 ft - 6 in. off each adjacent wall. This results in an area of coverage per sprinkler of 225 sf which is the maximum. The 6 ft dimension is imposed solely based on the maximum area of coverage for two sprinklers. Once you have selected a wall that you exceed the 7'6" restriction, you are set in that direction and cannot exceed the 7 ft - 6 in. maximum in any other direction. In other words, if you space the sprinkler 8 ft - 0 in. off one wall, you cannot then also be 8 ft - 0 in. off the opposite wall even though 16 ft - 0 in. is less than the 16 ft - 6 in. resulting when you're 9 ft - 0 in. off one wall and 7 ft - 6 in. off the other. Another limitation that should be noted is that the total room area cannot exceed 800 sf.

-----------------
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees.

Copyright (c) 2007, American Fire Sprinkler Association. All Rights Reserved
--------------------------
If you'd rather not receive future faxes from AFSA, fax your removal request to Linda Dawson at Efax (214) 242-3155 or call toll free (888) 839-4830 or send e-mail request @ [EMAIL PROTECTED] Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful.