American Fire Sprinkler Association
12750 Merit Dr., Suite 350 Dallas TX 75251
Ph:  (214) 349-5965       Fax:  (214) 276-0908

-------------------------
TECHNICAL UPDATE
September 13, 2007
-------------------------

"We are installing a NFPA 13R system for a group home. The water supply is from a rural water system. The type of master meter they used is not listed for fire protection service. How are other areas of the country addressing this situation?"

We have reviewed the 2007 Edition of NFPA 13R that you have identified as the applicable Code or Standard. Our informal interpretation is that the meter does not have to be "listed for fire protection"; it only has to be in compliance with the local plumbing code.

Unless modified by a local amendment, NFPA 13R only requires that the water supply to the automatic sprinkler system be in complaisance with the local plumbing code. This is indicated by the fact that section 6.6 on Water Supplies does NOT require the underground to be installed in accordance with NFPA 24 nor does it require any of the underground components to be listed. The only guidance is in the Annex section A.6.6.3. It states that the connection to city mains for fire protection is often subject to local regulation of metering and backflow prevention requirements. Also the flow characteristics of the meter are to be included in the hydraulic calculation of the system. As such, as long as the meter meets the requirements of the plumbing code (and is large enough to meet the identified sprinkler demand) it is acceptable.

-----------------
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees.

Copyright (c) 2007, American Fire Sprinkler Association. All Rights Reserved
--------------------------
If you'd rather not receive future faxes from AFSA, fax your removal request to Linda Dawson at Efax (214) 242-3155 or call toll free (888) 839-4830 or send e-mail request @ [EMAIL PROTECTED] Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful.

_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to