American Fire Sprinkler Association
12750 Merit Dr., Suite 350 Dallas TX 75251
Ph: (214) 349-5965       Fax: (214) 276-0908

------------------------------
TECHNICAL UPDATE
September 5, 2007
------------------------------

"I have a scenario in a 53 story high-rise building where there are pressure reducing valves servicing zone controls, pressure regulating valves servicing hose valves, and a high pressure pump servicing the entire sprinkler system. Is there a visible way to determine a floor level at which one could stop utilizing the pressure reducing and pressure regulating valves?"

We have reviewed NFPA 13, 2002 edition and NFPA 14, 2003 edition, and NFPA 20, 2003 edition as the applicable standards. Our informal interpretation is that generally the upper six to ten stories will be less than 175 psi depending on the hydraulic calculations and the supply from the fire pump.

The requirement from NFPA 14 is that the two most remote outlets on the standpipe must have a minimum of 100-psi outlet pressure while flowing 500 gpm. The maximum outlet pressure from 11/2 in. hoses is 100 psi and 175 psi for other hose sizes according to section 7.8.3.2. This along with additional standpipe risers is the driver for the remainder of the design. When determining if pressure- reducing valves are needed, also consider the pressures created from the pump during churn. We know that from NFPA 20 that the fire pump should not exceed 140% of the rated pressure while at churn but this will vary depending on the impeller used. So, if the pump must supply at least 100 psi from the outlet while flowing 500 gpm, the pressures created at churn can be from 120 to 140 psi. Since fire sprinkler and fire hose components are rated at 175-psi maximum pressure, this leaves a pressure difference of 35 to 55 psi from the churn pressure. A calculation of these pressures to elevation (divide by 0.433 psi/ ft) shows approximately 80 ft and 127 ft. If there is 12 ft per story, then this equates to roughly six to ten stories. The other consideration is the pressure from the outlet of the Class I hose connections where the NFPA 14 standard caps it at 175 psi. Be aware that if 175 psi is provided from the hose outlet for firefighting use, the hose will be so hard or stiff that the firefighters will not be able to bend the hose, thus reducing the capability of the firefighting operations. Section 5.1.2 requires that the authority having jurisdiction shall be consulted regarding the required type of system, class of system, and special requirements and this is an opportunity to discuss the acceptable maximum outlet pressures from the hose valves. This may lead to pressure reducing valves needed for hose valves on the upper floors but not necessarily on the sprinkler systems. In closing, there are several factors affecting where pressure reducing valves are placed but generally the upper six to ten stories will not require them.

-------------------
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees.

Copyright (c) 2007, American Fire Sprinkler Association. All Rights Reserved
--------------------------
If you'd rather not receive future faxes from AFSA, fax your removal request to Linda Dawson at Efax (214) 242-3155 or call toll free (888) 839-4830 or send e-mail request @ [EMAIL PROTECTED] Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful.