American Fire Sprinkler Association
12750 Merit Dr., Suite 350 * Dallas TX 75251
Ph: (214) 349-5965       Fax: (214) 276-0908

------------------
TECHNICAL UPDATE
November 28, 2007
------------------

"We have a storage facility protected by both ESFR system and an adjacent system with standard response spray sprinklers. Does extending the ESFR protection 15 ft into the adjacent area per 12.3 eliminate the need for the draft curtain per 8.4.6.4?"

We have reviewed NFPA 13, 2007 edition that you identified as the applicable standard. Our informal interpretation is that the draft curtain is also required.

Sections 12.3 and (12.1.5, 2002 ed.) requires the design basis to extend 15 ft past the edge of the higher demand so that the overlapping discharge will be adequate. The requirements of Section 8.4.6.4 address the issue of heat flow from any fire and are not affected by a corresponding hazard/discharge relationship. The draft curtain is meant to keep the adjacent ESFR sprinklers from activating before the spray sprinklers over the fire due to their lower thermal response. For this to actually work, a fire cannot occur beneath the draft stop. That's why there is an additional requirement for a clear aisle directly beneath the draft stop.

----------------- Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees.

Copyright (c) 2007, American Fire Sprinkler Association. All Rights Reserved
--------------------------
If you'd rather not receive future faxes from AFSA, fax your removal request to Linda Dawson at Efax (214) 242-3155 or call toll free (888) 839-4830 or send e-mail request @ [EMAIL PROTECTED] Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful.