"WHEN HYDROSTATICALLY TESTING NEW UNDERGROUND PIPING CAN THE PRESSURE DROP BELOW 200 PSI? OUR TEST DROPPED TO 192 PSI BEFORE PUMPING IT BACK UP TO 200 PSI IN ORDER TO DEFINE THE AMOUNT OF LEAKAGE."

We have reviewed NFPA 13, 2002 edition that you identified as the applicable standard. Our informal interpretation is that the test can drop below 200 psi.

The confusion on the issue is probably stemming from the standard being a little casual in their description of the test in 10.10.2.2.1. In this section it says "shall maintain the pressure without loss for 2 hrs". I believe the committee, in an effort to better coordinate the text with that for above pipe, inadvertently included the above text. I say this since it is physically impossible to apply the allowed leakage in 10.10.2.2.4 without a minor loss in pressure. Underground pipe has slip-on joints as well as other components such as valves that allow leakage. Although also worded a bit odd, 10.10.2.2.4 (4) tells us that in evaluating the amount of leakage we must use a calibrated container to determine the volume of water and that we must pump the pressure back up to the specified amount in order to complete the test. For instance, if your test started at 220 psi due to a higher operating pressure, you couldn't pump the system back to 200 psi when determining the amount of leakage.


-----------------
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees. Copyright (c) 2007, American Fire Sprinkler Association. All Rights Reserved
--------------------------
If you'd rather not receive future faxes from AFSA, fax your removal request to Linda Dawson at Efax (214) 242-3155 or call toll free (888) 839-4830 or send e-mail request @ [EMAIL PROTECTED] Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful. _______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to