American Fire Sprinkler Association
12750 Merit Dr., Suite 350 Dallas TX 75251
Ph:  (214) 349-5965       Fax:  (214) 276-0908

------------------
TECHNICAL UPDATE
January 3, 2008
------------------

What is the minimum section pressure for a centrifugal pump when tested at 150 percent?"

We have reviewed the 2007 Edition of NFPA 20 as the applicable Standard. Our informal interpretation is that gauge pressure at the suction flange shall be 0 psi or higher at 150 percent of the rated capacity of the pump.

Some AHJ's or water companies will set a minimum of 10 to 20 psi residual pressure for the city main. This is to avoid the potential for ground water seeping into the distribution supply. There is no such requirement in NFPA 20 for 10 or 20 psi on city mains. Section 5.14.3.1 does establish that the gauge pressure at the pump suction flanges shall be 0 psi or higher with the pump operating at 150 percent of rated capacity. Some AHJ's are also requiring backflow prevention devices in the suction line. Section 5.26.4 indicates that where a backflow prevention device is installed, the final arrangement shall provide effective pump performance with a minimum suction pressure of 0 psi at the gauge at 150 percent of the rated capacity. If the suction supplies do not permit flowing at 150 percent, the final arrangement shall provide effective pump performance at the maximum allowable discharge. However, the discharge shall exceed the fire protection system design flow. Suction pressures are also indicated for conducting an acceptance test. Section 14.2.7.2.2 will allow for test flows lower than 150 percent if the available suction supplies do not permit the flowing of 150 percent. The reduced capacity shall constitute an acceptable test, provided that the pump discharge exceeds the fire protection system design flow and pressure requirements. Another factor to consider in the suction pipe is velocity. The velocity in the suction pipe cannot exceed 15 ft/sec as indicated in section 5.14.3.3. Using the pipe sizes established in Table 5.25 will assure that the velocity of 15 ft/sec in the suction pipe will not be exceeded.

-----------------
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees.

Copyright (c) 2008, American Fire Sprinkler Association. All Rights Reserved
--------------------------
If you'd rather not receive future faxes from AFSA, fax your removal request to Linda Dawson at Efax (214) 242-3155 or call toll free (888) 839-4830 or send e-mail request @ [EMAIL PROTECTED] Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful.