American Fire Sprinkler Association
12750 Merit Dr., Suite 350 Dallas TX 75251
Ph: (214) 349-5965       Fax: (214) 276-0908

-------------------
TECHNICAL UPDATE
January 16,2008
-------------------

"I have a non-combustible canopy over a loading dock. Is there no limitation on the width of the canopy in regards to sprinkler protection below?"

We have reviewed 2002 edition of NFPA 13 that you indicated as the applicable standard. Our informal interpretation is that sprinklers must be provided under noncombustible canopies regardless of width where combustibles are stored and handled.

Section 8.14.7.4 indicates that when a noncombustible canopy is located over combustibles that are stored or handled, sprinklers must be provided. This section would be clearer if it ended with "regardless of width." This would indicate that Section 8.14.7.1 would not apply when it references that sprinklers shall be installed under exterior roofs or canopies exceeding 4 ft in width. The commentary text from the Handbook under Section 8.14.7.1 indicates that canopies less than 4 ft in width do not need to be sprinklered regardless of construction type provided no combustibles are stored beneath them. So when combustibles are stored and handled under the noncombustible canopy, then sprinklers must be provided regardless of the width or construction of the canopy. The section does not indicate the amount of combustibles that must be present. Note that the annex material A.8.14.7.4 addresses combustible storage or handling that is not sufficient to justify sprinklers and it states, "Short-term transient storage, such as that for delivered packages, and the presence of planters, newspaper machines, and so forth, should not be considered storage or handling of combustibles." There is no change to the application of this situation in the 2007 edition except for additional clarification on vehicles. When they are temporarily beneath a canopy, such as a bank drive-in, or even temporarily parked, such as hotel porte-cocheres, they are not considered storage. This can be found in the 2002 edition of the Sprinkler Handbook and is now in 13:A.8.15.7.2 in the 2007 edition.
-----------------
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees.

Copyright (c) 2008, American Fire Sprinkler Association. All Rights Reserved
--------------------------
If you'd rather not receive future faxes from AFSA, fax your removal request to Linda Dawson at Efax (214) 242-3155 or call toll free (888) 839-4830 or send e-mail request @ [EMAIL PROTECTED] Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful.