TECHNICAL UPDATE
January 30, 2008
_________________________


"Are you required to add the domestic water demand (showers, washer, bathtub, etc.) to the hydraulic calculations for a NFPA 13D type system?"

We have reviewed the 2007 Edition of NFPA 13D that you have identified as the applicable Standard. Our informal interpretation is that a sprinkler system for a single dwelling unit will not require any inclusion for domestic demand.

There is only one type of installation that requires including a domestic demand with the sprinkler calculation. A multipurpose system that consists of a common supply main providing both domestic and sprinkler water AND serving more than one dwelling unit will require the inclusion of 5 gpm for domestic demand. This requirement comes from Subsection 6.3 (1). An allowance for the exclusion of the domestic demand is permitted if means are provided to prevent flow into the domestic water system upon operation of a sprinkler. This can be accomplished by installing a residential domestic shutoff valve that will automatically shutoff the supply to the domestic system when a sprinkler activates. The residential domestic shutoff valve is only available in the 1-inch size according to the manufacturer.

-----------------
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees.

Copyright (c) 2008, American Fire Sprinkler Association. All Rights Reserved

--------------------------
If you'd rather not receive future faxes from AFSA, fax your removal request to Linda Dawson at Efax (214) 242-3155 or call toll free (888) 839-4830 or send e-mail request @ [EMAIL PROTECTED] Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful. _______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to