January   2008
--------------------

NEW FORMAT REQUIRED FOR HYDRAULIC CALCULATIONS
If you are operating under the 2007 edition of NFPA 13, Standard for the Installation of Sprinkler Systems, you'll likely need to update your software for hydraulic calculations. Effective January 1, 2008, the format of the hydraulic information, including the order of the forms, must be provided as dictated in Section 22.3.5 of the 2007 edition of NFPA 13. The information from the hydraulic calculations is not new. The new requirement standardizes the format in which the information is presented to provide consistency from each computer program or set of hand calculations to aid the plan reviewer or Authority Having Jurisdiction in the plan review process. The software providers for hydraulic calculation programs participated in the development of the output format, so they are aware of the requirement. Check the building code that has been adopted by your state or local jurisdiction to verify the applicable version of NFPA 13 that is in effect. The NFPA 13 edition in effect could be one or two cycles behind the most recent edition. For example, the International Building Code (IBC) 2003 edition references the 1999 edition of NFPA 13, IBC 2006 edition references the 2002 edition of NFPA 13, and the 2006 Life Safety Code(r) references the 2002 edition of NFPA 13. Also be aware that local amendments can specify the edition of NFPA 13 that is in effect. If you aren't yet applying the 2007 edition, you may want to check the implementation schedule.

GALVANIZED PIPE - WHEN IS IT REQUIRED FOR USE IN NFPA 13 APPLICATIONS?
There is some misconception that all dry pipe systems are required to have galvanized piping. Not so according to the 2007 edition of NFPA 13. Dry pipe systems can be black steel except for a few applications. The dry pipe system piping must be corrosion resistant or internally galvanized when small orifice K-factor 4.2 sprinklers are used according to Section 8.3.4.3. Dry pipe systems and preaction systems using large drop sprinklers requires internally galvanized pipe according to Section 8.4.7.2. Water cooling towers under the Special Occupancy Requirements Chapter in Section 21.24.2.10.1 requires the piping, fittings, hangers, braces, and attachment hardware including fasteners shall be hot-dip galvanized steel or use other materials that have a superior corrosion resistance. Two other sections that require galvanized pipe is Section 6.9.3.3 that requires all piping to water motor-operated devices shall be galvanized or brass or other corrosion-resistant material acceptable under this standard, and Section 6.9.3.3 that piping between the sprinkler system and a pressure-actuated alarm-initiating device shall be galvanized or of nonferrous metal or other approved corrosion-resistant material. Thus there is no requirement carte blanche that all dry pipe system must have galvanized piping.

NFPA 14 - STANDARD FOR THE INSTALLATION OF STANDPIPES AND HOSE SYSTEMS IS ACCEPTING PROPOSALS It seems like the 2007 edition of NFPA 14 just arrived, but NFPA is accepting proposals for the 2010 edition of NFPA 14. The Proposal Closing date is May 30, 2008. Now is the time to review the document and submit new requirements, changes, or clarifications for the committee's consideration.
--------------------
Mark your calendars for the next Virtual Seminar
Fire Pumps
January 31, 2008
To Register:  Event ID: 13654

12:00 PM EST
11:00 AM CST
10:00 PM MST
 9:00 AM PST
Earn:  0.15 CEU's  / 1.5 CPD's.
Member:  $90 per connection
Non Member:   $130 per connection
CEU Certificate: $40 per listener to receive CEU Certificate.

If any listeners at your site need CEU/CPD credit, the processing fee is an additional $40 per person. Enter each person's full name and e- mail address you are purchasing CEU/CPD credits for including yourself to receive Certificate.

To Register:
Online: www.krm.com/afsa
By Phone: 800-775-7654, please have your credit card information ready.
By Fax: 800-676-0734.  Fax completed form with Credit Card information.
By Mail: KRM Information Services Inc. PO Box 1187 Eau Claire, WI 54702-1187 (Payment must accompany registration)


2008 AFSA DESIGN SCHOOLS
Beginning System Planning School
February 4-15, 2008 SOLD OUT!
March 3-14, 2008
April 14-25, 2008
May 12-23, 2008
June 16-27, 2008
July 14-25, 2008
August 11-22, 2008
September. 22-October. 3, 2008
November 3-14, 2008.
Registration Prices:    Member  $1100        Non-Member   $1600
NOTE: Enrollment open only to AFSA Contractor Members until 6 weeks prior to each class.
--------------------
TechTalk is prepared by the Technical Services Department of the American Fire Sprinkler Association: Vice President of Engineering and Technical Services, Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a CFPS and a NICET IV certified automatic sprinkler technician, and Tom Wellen, a degreed fire protection-engineering technologist. Opinions are provided with the understanding that AFSA assumes no liability for the opinions or actions taken on them and they are not to be considered the official interpretation of the NFPA or that of its technical committees.

Copyright (c) 2008, American Fire Sprinkler Association, 12750 Merit Drive, Ste 350, Dallas, TX 75250 Voice (214) 349-5965 ext 124 or Fax (214) 343-8898. All rights reserved.

If you'd rather not receive future faxes from AFSA, fax your removal request to Linda Dawson at Efax (214) 242-3155 or call toll free (888) 839-4830 or send e-mail request @ [EMAIL PROTECTED] Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful.


 _______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to