American Fire Sprinkler Association
12750 Merit Dr., Suite 350 Dallas TX 75251
Ph: (214) 349-5965        Fax: (214) 276-0908

----------------------------
TECHNICAL UPDATE
May 21, 2008
----------------------------

An elevation diagram was provided showing the piping arrangement for suction and discharge of the fire pump. You asked the following question:

“Is it acceptable to have one tee, which is less than 10 diameters of the suction pipe to the inlet flange of the fire pump with center line plane of the tee parallel to the fire pump split-case pump shaft? This is based on the situation that the water goes straight through the tee and the side outlet of the tee is to feed the by-pass which is closed when fire pump is in service.”

We have reviewed the 2007 edition of NFPA 20 that you indicated as the applicable Standard. Our informal interpretation is that the tee fitting will not affect the water going into the fire pump. However, when a bypass is provided the valves shall be in the open position.

The purpose of the tee is to supply water through the side outlet to supply the fire pump bypass. The tee fitting does not feed water from the side outlet into the suction line of the fire pump thus the requirements of Section 5.14.6.3 do not apply. As you said, the water will flow straight through the tee fitting. Another tee fitting is shown upstream of the tee fitting in question and connects with an existing 8 in. city water supply. The tee fitting outlet centerline is located to be perpendicular to the split-case fire pump shaft. This tee fitting orientation meets the requirements of Section 5.14.6.3. This requirement is to help prevent turbulence from the water exiting the elbow or tee from exerting undue stress on the fire pump’s impeller. If the centerline of the elbow or tee is vertical (perpendicular) to the pump shaft, this stress is significantly reduced. This issue is clarified in Section 5.14.6.3.3 that states, “Elbows with a centerline plane perpendicular to the horizontal split- case pump shaft shall be permitted at any location in the pump suction intake.” This is further illustrated in Figure A.5.14.6, which shows an acceptable piping arrangement as having a suction supply dropping down to an elbow that is directly attached to the suction side flange of the pump.

Regarding the valve for the bypass connection, it shall always be open according to Section 5.16.1. If a bypass is provided, the valves shall be supervised in the open position. The loss of the pump can occur not only from maintenance, but also equipment or power failure where the bypass connection would be beneficial. In addition, since some of the suction and discharge piping is not as cleanly arranged as a new installation, it may be worthwhile passing along the design arrangement to the pump manufacturer’s representative to ensure the existing piping arrangement would not effect the operation of the pump.
-----------------
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees.

Copyright © 2008, American Fire Sprinkler Association. All Rights Reserved
--------------------------
If you’d rather not receive future faxes from AFSA, fax your removal request to Linda Dawson at Efax (214) 242-3155 or call toll free (888) 839-4830 or send e-mail request @ [EMAIL PROTECTED] Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful.


_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to