"We plan to replace six existing upright sprinklers with six pendents on flexible hose fittings. Are hydraulic calculations required?"



We have reviewed the 2007 edition of NFPA 13 that you indicated as the applicable Standard. Our informal interpretation is that hydraulic calculations will be needed.



If it is not apparent that the modifications have resulted in a less hydraulically demanding configuration, it is the AHJ's prerogative to require hydraulic calculations for the modified area. Section 8.15.19.5 addresses the requirement when modifying (revamping) a hydraulically calculated system. Unlike the pipe schedule system, this requires that hydraulic calculations be performed to verify that the design flow rate will be achieved. The sprinkler handbook confirms that when a hydraulically designed system is modified, new calculations must be provided. The change from standard sprinklers to a flexible hose fitting will create a modified K-factor in the system. As such, modifications to an existing system from standard spray sprinklers would require new calculations just like changing from standard to extended coverage sprinklers. In addition, when you relocate a sprinkler in a calculated system, it has been modified and the area of coverage of the sprinkler is likely changed. This could change the required design flow and pressure of the sprinkler. This is a very literal interpretation of NFPA 13. Some AHJ's require calculations for any relocated sprinkler, while most set a threshold of 5, 10 or 15 relocated sprinklers before they will require calculations. I would suggest that you consult with your AHJ to see at what point that calculations are required. The factors that may be discussed include the equivalent feet for friction loss of the flexible hose fitting and the safety factor between the water demand and the available water supply. Many jurisdictions do not require calculations because they recognize that changes to the assigned area of coverage is typically small and the greater pressure upstream from the end head produces a discharge greater than the required minimum.



-----------------

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees.



Copyright (c) 2008, American Fire Sprinkler Association. All Rights Reserved

--------------------------

If you'd rather not receive future faxes from AFSA, fax your removal request to Amy Sweeney at Efax (214) 242-3155 or call toll free (888) 839-4830 or send e-mail request @ [EMAIL PROTECTED] Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful.



_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to